Discuss And another mad question ("minimum current") in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
17
28. Which one of the following is not considered when calculating the minimum current carrying capacity of live
conductors of a cable?
a Ambient temperature.
b Grouping.
c Type of protective device.
d The maximum permitted volt drop.
 
Good stuff find device rating divide by factors, look up increased calculated current against correct table and check install method column choose nearest highest value. Then worry about volt drop
 
The way I read the question is you would select the cable on the size of protective device so it would have a bearing on it. Ib<In<Iz
So with a 20A radial, what effect would the 20A protective device have on the CCC of the cable used to wire the circuit?

Better still, consider designing a cooker or a shower circuit.
What is the first thing you need to know?
 
Last edited by a moderator:
But ask yourself why do you put the 20A MCB on that radial??
First you need to know the total design current for the circuit. For arguments sake say 7A of lights on a radial. You would then choose your protective device based on this calculation. So say you choose a 10A 60898MCB, forgetting derating factors for now you would then choose a cable with a current carrying capacity higher than the protective device chosen.
The only thing not needed in the OP question for CCC calcs is VD
 
You take a protective device of current rating C, the minimum current carrying capacity of a live conductor connected to this protective device is C (or 0.725C for semi enclosed fuses), however the cable is grouped with other cables so limiting the current that can be taken on the live conductors so now the minimum CCC is C/cg, but the cable is in a high ambient temperature so the minimum CCC of the cable is now C/cg*ca.
The minimum to which the current carrying capacity of the cable can be taken is C/cg*ca therefore you have calculated the minimum CCC of the live conductors by taking into account the type of protective device, the ambient temperature and the grouping.
The volt drop does not enter into the CCC calculation, it may be very relevant for compliance but not for current carrying capacity.
 
I’ve read your post Richard but surely the very fact it is the current carrying CAPACITY implies a maximum. And the cables capacity must be above that of the protective device.
It just doesn’t work as a minimum?
You take a protective device of current rating C, the minimum current carrying capacity of a live conductor connected to this protective device is C
Surly if a protective device is C then the CCC of cable has to be above C but as for the minimum, it could be anything you want just so long as the protective device will trip before the maximum is reached.

Maybe we are getting at the same thing and I’m missing your meaning? Maybe it’s time for another glass of red. Now where did I put the other bottle.
 
Whilst the rating of the protective device should be no greater than the CCC of the cable, the tripping current of the device should also not be greater than 1.45 times the CCC of the cable.
 
Ohhh I see so by minimum they are talking what's the minimum that will do the job, the wording is bad it should say calculate the minimum required capacity live conductor current for the circuit.
 
Last edited:

Reply to And another mad question ("minimum current") in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
676
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
475
not to sure on how to find the wats for the power cable calcs could anyone help me its for a ring with 3 Dubble sockets on DB05-3L2 cable size...
Replies
4
Views
1K
Hi Guy's, I'm revising for my 18th amd 2 and came across a question that has me a little confused. I think its probably the question is badly...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock