Search the forum,

Discuss Any ideas Please in the Commercial Electrical Advice area at ElectriciansForums.net

M

mayfair

Hi Guys
Been to a warehouse today large cooler room main MCB 40A 4 pole N L1L2L3 plus 40A 30ma Diff it all works fine until the compresor shuts off then the Main MCB trips ...not the diff the mcb if you put i back on all is fine even if compresor dont start. Any thoughts my brain hurts.
Cheers
Gary
 
One thought, it could be possible when the compressor for the fridge stops the stat is energised because it needs to take over to maintain the temperature and it could be faulty and shorting out hense the short circuit and the fact the MCB is blowing, then again it may be something completely different.
 
Is the compressor contactor operating anything when in the off position like a sump heater or defrost element that could have a fault maybe?

Can you upload some pics of the controls?
 
Looks like (Fingers crossed) it was the thermostat arcing not done it since it was changed at 8.00 am this morning still dont know why the rcd didnt drop out ramped it and seems ok. As my old lecturer used to say its fixed be happy with that and stop foofing around with it now. Thanks for input apart from #2 which i still dont understand
 
Looks like (Fingers crossed) it was the thermostat arcing not done it since it was changed at 8.00 am this morning still dont know why the rcd didnt drop out ramped it and seems ok. As my old lecturer used to say its fixed be happy with that and stop foofing around with it now. Thanks for input apart from #2 which i still dont understand
So I was right then?
 
Glad it's up and running again although I'm not sure why an arcing t/stat would be the cause. I enjoy refrigeration work, it's interesting controls and it makes a nice change to the run of the mill stuff.
 

Reply to Any ideas Please in the Commercial Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock