Discuss Are you based in Frimley???????? in the UK Electrical Forum area at ElectriciansForums.net

O

Octopus

So I got a call from a customer asking me about something I did in Feb 16 - so I duely paid a visit. Knowing they had had some work done I asked if I could see the certificate..... as I didn't take mine with me!

Now bearing in mind a new fuseboard had been fitted, the kitchen had been hacked around, downlights had been fitted and a wall removed I was expecting an detailed EIC........

Er no, the EIC simply said replacement fuseboard..... which had all 10 "slots" used.

This is a photo of the test results sheet.........

Test results.jpg


Sorry its side ways

Anybody want to play "spot the mistake / ommision / unusual entry" with me?
 
Ring final 9 appears to be rather long and open circuit on the lines. Seems they didn't loop it either or several of the others.
They also have 4.0 cpcs on the 6.0 cables, assuming T&E.
No IR readings.
 
Dear me, I could have fabricated a better test sheet sitting at home with a cuppa!
Not supposed to put LIM on an EIC.
There's and old saying "If it looks right, then it is right"
This clearly isn't right.
 
It's not just you ... I'd be suggesting to Client the last lot should return and provide one done to standard. If they hesitate, perhaps offer to email original to their CPS for review :rolleyes:
 
How can they tick polarity on the circuits they haven’t tested or entered results for R1+R2 or Max ZS reading? Ring Circuit 9 20000 so near enough useless continuity on R1, the list of errors and inconsistency just keeps getting worse. So what was the IPf at that board left blank too.
 
How is it applicable?
To start with, the form asks for the maximum allowed by BS7671.
I guess technically none of it is applicable as the certificate is for a board change.
I wonder why it’s applicable for one RCD, but not for the other two?
It’s also odd that they conducted no IR tests.
 
I was wondering about forwarding a copy to Elecsa .. I do have his details and number!
Maybe get the customer to get in touch with elecsa and send a copy of that cert complete with installer name and number and ask them to confirm if that certificate is genuine.
 
To start with, the form asks for the maximum allowed by BS7671.
I guess technically none of it is applicable as the certificate is for a board change.
I wonder why it’s applicable for one RCD, but not for the other two?
It’s also odd that they conducted no IR tests.
I think he means you don’t measure a zs for the rcd hence the box is marked N/A on the certificate for both.
Also why would you write 1667 ohms for a 30mA rcd for maximum zs when that referes to the touch voltages not rising above 50 volts it’s not really applicable to the certificate in my opinion, at least that is I’ve never wrote it in unless the rcd is proving fault protection as the sole means such as a TT system.
 
Last edited:

Reply to Are you based in Frimley???????? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
419
I have been asked to rewire an antique metal standard lamp. It has been rewired previously, but not earthed..! One of the screws on the base has a...
Replies
35
Views
5K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
946
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock