Discuss Are you based in Frimley???????? in the UK Electrical Forum area at ElectriciansForums.net

Zs of the circuits are measured
Rcd tests are carried out
Ze etc etc.
If the rcd is external to the main consumer unit then the distribution circuit supplying and connecting to the rcd is measured but no not the physical rcd no.
That’s what rcd tests are for is it not?
 
I wonder why it’s applicable for one RCD, but not for the other two?
The first one is an RCBO (61009), the other two are two RCDs (61008) covering a group of MCBs each. So the RCDs themselves don't require a Zs test, rather the MCBs they cover do. I think the way he has used a circuit to write down the RCDs is confusing.
 
Last edited:
The first one is an RCBO (61009), the other two are two RCDs (61008) covering a group of MCBs each. So the RCDs themselves don't require a Zs test, rather the MCBs they cover do. I think the way he has used a circuit to write down the RCDs is confusing.
Yep. I think someone's getting mixed up.
He's given the RCD's a circuit number. I usually replace the cct no with RCD 1 and RCD2 and leave a blank line, except for the RCD times and rating.
 
You have to know the Zs to ensure the RCDs will work.
<1667 Ohms for 30mA
<500 Ohms for 100mA
<167 Ohms for 300mA
<100 Ohms for 500mA.
You cannot say it’s not applicable.
You can leave it blank because you’ve tested all the circuits protected by the RCD, or you can record the highest measured value for the circuits the RCD protects.
 
You have to know the Zs to ensure the RCDs will work.
<1667 Ohms for 30mA
<500 Ohms for 100mA
<167 Ohms for 300mA
<100 Ohms for 500mA.
You cannot say it’s not applicable.
You can leave it blank because you’ve tested all the circuits protected by the RCD, or you can record the highest measured value for the circuits the RCD protects.
By taking a zs of the protected rcd circuits and even the ze then we know that 50v/0.03 is satisfied anyway however the zs is measured to ensure ADS of the over current protective device.
Nowhere does any literature on testing say that the rcd requires a separate zs test and why would it?
Any specific rcd testing can be found in GN3
It is the rcd tests that ensures the rcd will disconnect in the required times.
 
You have to know the Zs to ensure the RCDs will work.
<1667 Ohms for 30mA
<500 Ohms for 100mA
<167 Ohms for 300mA
<100 Ohms for 500mA.
You cannot say it’s not applicable.
You can leave it blank because you’ve tested all the circuits protected by the RCD, or you can record the highest measured value for the circuits the RCD protects.
I’m guessing your talking about rcd testing half times 1x and 5x tests and not a zs of the rcd as they are not the same.
 
You have to know the Zs to ensure the RCDs will work.
<1667 Ohms for 30mA
<500 Ohms for 100mA
<167 Ohms for 300mA
<100 Ohms for 500mA.
You cannot say it’s not applicable.
You can leave it blank because you’ve tested all the circuits protected by the RCD, or you can record the highest measured value for the circuits the RCD protects.
These values are for if you need the RCD to provide fault protection as well as additional protection. So in most situations they are not applicable.
 
UPDATE:

Here is the revised schedule:

Philip 2.png


But the installer has also issued a "danger notice"

Issueing "danger notices" - https://www.electriciansforums.co.uk/threads/issueing-danger-notices.124295/
 

Reply to Are you based in Frimley???????? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
452
I have been asked to rewire an antique metal standard lamp. It has been rewired previously, but not earthed..! One of the screws on the base has a...
Replies
35
Views
5K
Hi all -- full disclosure I am a 'DIY-er' but wanted to post here for greater visibility seeing as I certainly won't be doing this work myself...
Replies
21
Views
4K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
955
I hope this is the right place to post this, please redirect me if not. I've spent quite some time reading the forums, so I apologize if I've...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock