Discuss Back in the 2391 days in the Electricians' Talk area at ElectriciansForums.net

H

Hawkmoon

Short question (2006 paper):


'Small commercial unit owned by a paint company:

Supply characteristics as follows..
The supply forms a 400/230V 50Hz TN-C-S system. The main fuses are 100A BS 88-2 and measured value of PFC is 1600A. The earthing conductor is a 25mm copper conductor and the main equipotential bonding conductors to gas, water and structural steel are 16mm copper.

Determine Ze from the above information'


Remember this causing much confusion...

Answers?
 
Last edited by a moderator:
I'll be the first to put myself out on a limb.

The PFC would have been doubled so half that.

Then it's ohms law. Cannot see why the size if the eq bonding conducters are relevant as these are disconnected for Ze.

And the main earth conductor is also irrelevant as that is what it is.
 
but was it doubled or x 1.732? or even PEFC as opposed to PSCC??
 
Its a ---- question TBF. I've had a few over the past few weeks where you only get half a story and it's up to you to make assumptions.




Anyway got go to Los Santos.....
 
Last edited:
I can tell you I was told that approx 50% of students forgot the 3 phase aspect and applied ohms law to the 1600

Approx 20% went with 800


anyone else??
 
Last edited by a moderator:
I'll be the first to put myself out on a limb.

The PFC would have been doubled so half that.

Then it's ohms law. Cannot see why the size if the eq bonding conducters are relevant as these are disconnected for Ze.

And the main earth conductor is also irrelevant as that is what it is.


There were other questions relating to it in addition to the Ze issue
 
I'll be the first to put myself out on a limb.

The PFC would have been doubled so half that.

Then it's ohms law. Cannot see why the size if the eq bonding conducters are relevant as these are disconnected for Ze.

And the main earth conductor is also irrelevant as that is what it is.


Respect to you Lee - 80 odd views and you are the only one man enough to post up close to an answer lol

I got this wrong (not in exam but after in class where it was put up by a lecturer)
 
There should be a new qualification, City & Guilds 2399 'Initial verification and deciphering of vague exam questions'.

I've always thought their questions tend to be ambiguous and open to several interpretations in a large number of questions I have come across.
Not very helpful when you are under pressure in an exam situation!
 
Assuming that a pfc can only be measured off a singles supply one at a time them doubled by calculation. I would work it out as 230v divided by 1600a pfc = 0.14 ze
 
The problem is clearly on how the PFC was measured. Which is not clear on the question, as it says 230/400. So you either go with 230 to give 0.14, or what I am leaning with 400 which is 0.25
 
The problem is clearly on how the PFC was measured. Which is not clear on the question, as it says 230/400. So you either go with 230 to give 0.14, or what I am leaning with 400 which is 0.25
why would you go with 0.25 on 400v ? Is it because it feels better but it wrong
 

Reply to Back in the 2391 days in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K
Someone asked about abbreviations used here. So I tried to copy a list I made elsewhere: A/C Air Conditioning AC Alternating Current ACB...
Replies
41
Views
5K
Copied this from trainee section to see if I can get an answer, it is talked about a lot on the forum but reading through the old posts I can't...
Replies
40
Views
7K
Deleted member 26818
D
Afternoon in the middle of doing my 1st quote for a com/ind setup- bit out of my domestic comfort zone etc! it is for additional power in...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock