Discuss Back up generator on domestic in the UK Electrical Forum area at ElectriciansForums.net

growler

-
Arms
Reaction score
194
A customer has asked me to connect his back up generator 'properly' as currently he just flicks the main switch and plugs straight into the down stairs ring main.
I admit I have little experience with this and won't take it on unless I'm 100% I'm doing it correctly. It's a 5.5kva generator on a tt.
Can somebody help me with what I need to consider ?
So far I'm thinking
- change over switch
- earth electrode
 
Here we go.
1) your change over switch MUST disconnect Phase/ neutral AND EARTH from your DNO supply
2) Install an earth rod or mat connected to the frame of the genny
3) Link Neutral and Earth in the alternator
4) Unless the alternator has a method of maintaining the correct voltage / frequency, ie an AVR, do not connect any electronic equipment to the output
 
I will give you two other bits of advice,free. 1) your geny is of the wrong type and undersize, 2) Your customer will not pay what you will require to do it properly.....the distance between using the ubiquitous double plug top lead,and the correct system,is about the price of a month cruise to somewhere expensive...bon appetit
 
I personally wouldn't worry about disconnecting the earth, as you're always going to have inadvertent connections via bonding, CPC's and the general mass of earth, between your genny rod, and the DNO earth. In this instance, being a TT system, you needn't disconnect the earth anyway.
 
I will give you two other bits of advice,free. 1) your geny is of the wrong type and undersize, 2) Your customer will not pay what you will require to do it properly.....the distance between using the ubiquitous double plug top lead,and the correct system,is about the price of a month cruise to somewhere expensive...bon appetit

Would you care to expand on any of this?

How do you know what type of generator the OP's customer has?
Why do you say that 5.5KVA is too low for domestic backup?
Since the earthing is TT and is likely to already have adequate RCD earth fault protection, why should doing it properly cost the price of a month's cruise?
 
Here we go.
1) your change over switch MUST disconnect Phase/ neutral AND EARTH from your DNO supply
2) Install an earth rod or mat connected to the frame of the genny
3) Link Neutral and Earth in the alternator
4) Unless the alternator has a method of maintaining the correct voltage / frequency, ie an AVR, do not connect any electronic equipment to the output


Why would you need to disconnect the DNO earth, come to that,...how would you??
 
You can’t rely on the DNO earth as work could be ongoing on the LV system. But as this is TT it’s not a problem.
As Phil has said a positive change over is needed for both L&N.
Linking N&E makes the installation when running on the generator TN-S.
 
Why would you need to disconnect the DNO earth, come to that,...how would you??

During a power outage, you cannot assume the DNO's earth is intact or your own earth rod. Theres also the possibility that the genny will send a voltage down the DNO earth.
The 2poles and earth go to the 'Mains' side of the change over switch / contactor before going to the DB.

- - - Updated - - -

You beat me to it Tony
 
During a power outage, you cannot assume the DNO's earth is intact or your own earth rod. Theres also the possibility that the genny will send a voltage down the DNO earth.
The 2poles and earth go to the 'Mains' side of the change over switch / contactor before going to the DB.

- - - Updated - - -

You beat me to it Tony

What are you saying, ...that a 3 pole C/O switch is needed for a single phase supply??
 
I'm not sure what's more dangerous, me connecting up generators or customer continuing to connect generator via 3pin plug straight into the ring main ..
 

Reply to Back up generator on domestic in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just a query. As people have been asking me about changeover switches and generators. If a domestic house already has PV solar, and customer...
Replies
9
Views
2K
My house had previously been wired for a generator (probably not by code to this day) but previous homeowner disconnected and instead hooked up...
Replies
1
Views
530
Hi All Had an enquiry about installing a generator fed UPS to a house. I have a minimal amount of experience with UPS but am certainly no expert...
Replies
3
Views
1K
A customer has asked me to install a generator to supply her house for when they have a power cut. I have already said this is beyond my...
Replies
13
Views
6K
I want to use a manual change over switch to safely connect a 21kVA single phase tractor PTO powered generator to my mains supply in case of...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock