Your fan works by having two lives.
One live is permanently on, the other is switched by the light switch.
You turn on the light, the fan starts.
When you turn off the light, the switched live to the fan is turned off, the permanent live then powers the timer.
If you get the two lives mixed up, the fan wil usually just turn on and off with the light, it will not continue after the light is switched off.
The switch you have got can only switch one live.
You have connected the other live to the earth terminals.
 
Your fan works by having two lives.
One live is permanently on, the other is switched by the light switch.
You turn on the light, the fan starts.
When you turn off the light, the switched live to the fan is turned off, the permanent live then powers the timer.
If you get the two lives mixed up, the fan wil usually just turn on and off with the light, it will not continue after the light is switched off.
The switch you have got can only switch one live.
You have connected the other live to the earth terminals.


It made more sense now.....thank you very much.....
 
so if you had screwed the original switch to the back box (and had the back box been metal) it could have been a big bang!
 
better a big bang than an electrocuted DIYer (2nd thoughts, DIYers should be shot. :D:D:D.)
 
Yeso? Here? In the UK? Crikey...Brexit has been overturned!
and by the way Tel, I have been shot many times, but us pirates are made of sterner stuff, even us DIYers!
 
Yeso? Here? In the UK? Crikey...Brexit has been overturned!
and by the way Tel, I have been shot many times, but us pirates are made of sterner stuff, even us DIYers!
problem there is that pirates should not be shot. it just makes them angry.only solution is to hang them dancing from the nearest yardarm. :D:D:D.
 

Reply to Bathroom extractor switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I've installed a replacement bathroom extractor fan. Pic on the left is the old one. Pic on right is the new one. Wired the same way but the fan...
Replies
4
Views
898
HI There, I would be grateful if you could help me, I have a very long duct between the bathroom and extractor outlet vent and for sometime, the...
Replies
3
Views
1K
I’m replacing an old 100mm extractor fan in the kitchen with a new one. The old one was a pull cord fan whereas I bought a timer one (no pull...
Replies
3
Views
381
Hi all, I'm in the UK and have recently had a ducted extractor fan Mixflo 200W with timer fitted. The fan comes on with the pull cord and runs for...
Replies
6
Views
286
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
564

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock