in the old bpg4 it stated
Absence of supplementary bonding for installed Class II equipment where required (such as
in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future.
as:
Non-compliances with the current edition of BS 7671 that do not give rise to danger and do not require reporting.
In the new bpg4 (dec 2022) it only states:
Absence of supplementary bonding where required, in
a location containing a bath or shower, unless all of the requirements of Regulation 701.415.2 permitting omission are met is a :C2
Has the advice on class 2 only equipment in a bathroom been changed? or
would this be under “not required” as there are no simultaneously touchable exposed and extranous conductive parts
Absence of supplementary bonding for installed Class II equipment where required (such as
in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future.
as:
Non-compliances with the current edition of BS 7671 that do not give rise to danger and do not require reporting.
In the new bpg4 (dec 2022) it only states:
Absence of supplementary bonding where required, in
a location containing a bath or shower, unless all of the requirements of Regulation 701.415.2 permitting omission are met is a :C2
Has the advice on class 2 only equipment in a bathroom been changed? or
would this be under “not required” as there are no simultaneously touchable exposed and extranous conductive parts