Discuss best practice guide 4 (new edition) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

newfutile

-
Esteemed
Arms
Reaction score
388
in the old bpg4 it stated
Absence of supplementary bonding for installed Class II equipment where required (such as
in a location containing a bath or shower), in case the equipment is replaced with Class I equipment in the future.
as:
Non-compliances with the current edition of BS 7671 that do not give rise to danger and do not require reporting.

In the new bpg4 (dec 2022) it only states:
Absence of supplementary bonding where required, in
a location containing a bath or shower, unless all of the requirements of Regulation 701.415.2 permitting omission are met is a :C2

Has the advice on class 2 only equipment in a bathroom been changed? or
would this be under “not required” as there are no simultaneously touchable exposed and extranous conductive parts
 
TL;DR
coding EICR with BPG4
I would say the advice has been changed. Although in reality, the fact that the situation did not warrant a code nor did it require reporting, makes it a non-issue anyway.
 

Reply to best practice guide 4 (new edition) in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Don’t know if it’s been posted yet, but here’s a link to the new guidance for I&T from Electrical Safety First; Best practice guide 4...
Replies
2
Views
937
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
447
I have been asked by Trading Standards to carry out a report on some electrical work installed by another company (5 years ago). The 'new' wet...
Replies
31
Views
3K
I hope someone on here can help me with this. My 25-year-old daughter is buying a house with her partner, they are just about to exchange and...
Replies
22
Views
2K
Yes, it's another EICR coding question - hurrah! :blush: Inspecting a small 1 bed 70s ex-council flat that was going well. Main Bonding had...
Replies
12
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock