I have built a stable block consisting of two stables and a store. I have applied to have mains electricity installed, and as part p won't apply Iwill be wiring them myself. My question is do led strip lights have as much shadow as led floods. I have been using 12 volt floods, which are great but do cast shadows. I was thinking of fitting weather proof led strip lights, hoping they would be similar to the florescent strip lights. Any ideas?
 
Oh dear, seems like a little bit of knowledge and all that. The stable is in a field. No house on the land. No one lives in the stable, people that is, and it is not regularly occupied. It is therefore not a dwelling. BS7671 applies to dwellings, it says so clearly. If you think I am wrong, I will give you the name and address of my local council building control officer and you can correct him, as he confirmed the fact that BS7671 does not apply, and test and certificate was not required.
 
A little knowledge and all that indeed ....... but not on the side of the forum.

Here are the specific exclusions to BS7671 listed in Part 1. Can you see stables in it ?

2017-09-27 15.20.47.jpg
 
Static Zap, read my posts, the installation WILL be tested. I qualified as an electrician in 1965! Haha, still qualified enough to know how to test an installation, 50 years in the trade altogether, with local dno.
 
More to the point, can you show me where a building that is not a dwelling is covered? Unless it tells me that a non-dwelling is covered I couldn't give a hoot.
 
BS7671 applies to all electrical installations subject to the exceptions given by any78
have a read of section 705. i believe horses come under the general scope of livestock, even if i prefer them in a plate with chips, mushrooms and a touch of garlic.
 
Only applies to buildings covered by the regs, such as agricultural buildings that house livestock. I'll go with the planning officer, suits me. My animals are safe, probably safer than if the wiring was done by some of the registered sparks whose work I've seen.
 
stables come under the broader classification of agriculural and horticultural. just because the BS does not specifically mention stables per se.
polo mints are not advertised as containing a nitrogen/oxygen mixture, but we all know there's a hole in the middle, same as with your thinking.
 
So far only DPG had spoken any sense. Anyway, this time next week I will have my stables safely wired and connected to the mains. Certainly upset a few folk on here! Anyway, I'll agree to differ on the facts. I know I'm right, even if I'm not (and I am) so what? Life's too short to worry about details.
 
It's a bizarre concept that farms, farm buildings, cow sheds, chicken sheds, outbuildings should all be covered by the wiring regs, but for some reason stables specifically are excluded? Why on earth would you think that would makes sense?
 
It's a bizarre concept that farms, farm buildings, cow sheds, chicken sheds, outbuildings should all be covered by the wiring regs, but for some reason stables specifically are excluded? Why on earth would you think that would makes sense?
 
Still can't see stables mentioned, it's not commercial and it's not agricultural.

View attachment 38544

You can quite clearly see from the picture that you have provided that your earlier assertion that BS7671 applies only to dwellings is complete twaddle.

This should be enough evidence to consider that your understanding of the wiring regulations may not be as good as you thought. Certainly enough to consider wiring to the requirements of section 705.
 
You cannot assume that because stables aren't mentioned that they are included under some other heading. I get the point about livestock protection, but we don't have livestock only horses. The planning officer said if the building is not normally occupied, as in a dwelling, office, factory etc then BS7671 doesn't apply. Sorry to keep repeating myself, it is not commercial, not agricultural and we don't keep livestock.
 
Crazy argument. Stable next to a house needs to comply with regs, animals on a farm same, but your stable doesn't need to comply with any wiring regs at all. Yep, right.
So by your argument you could wire it all in bell wire and you are not contravening any regulations?
 
Google 'are horses livestock'. I have just come off the phone to my local planning officer. He has confirmed if the stable is on its own land, on it's own supply, and is not normally occupied then BS7671 does not apply.
 

Reply to Best type of lighting in stables in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock