Discuss boiler cross bonding in the UK Electrical Forum area at ElectriciansForums.net

Beer+Goggles_2aecec_4180379.jpg
 
we asked 100 electricians forum members, would it be correct to say, that on page 53 of the IET wiring regulations book, it is a requirement to main bond central heating and airconditioning systems?
 
When you say "we" do you mean "you" and when you say "asked 100 electricians" do you mean " I thought about it and made the answer up as I see it"?
 
we asked 100 electricians forum members, would it be correct to say, that on page 53 of the IET wiring regulations book, it is a requirement to main bond central heating and airconditioning systems?

Incorrect,

It is a requirement to main bond extraneous conductive parts, such as central heating pipes and aircon amongst other things.

So the requirement is to bond extraneous parts and the example of parts that might be extraneous includes central heating pipes and aircon.

There is also a section in the regulations which gives a definition of what an extraneous conductive part is.
 
well I had a relapse earlier in the week and the vet gave me more meds and yesterday I was a lot better.

Tidyboiler came over yesterday afternoon & we had good curry and she stayed over until teatime today. Before she left I went with her shopping at Sainsburys and managed to drive there and back in the MR2 and walk all around the place without my walking stick and wasn't too tired when we came back home so that was a big improvement so I've had a truly great day,thanks. :)

And we didn't leave a load of carnage, spill blood or have any assistants in tears! Result :dita:
 
we asked 100 electricians forum members, would it be correct to say, that on page 53 of the IET wiring regulations book, it is a requirement to main bond central heating and airconditioning systems?


Who's 'we' ?

You tell us, you're the expert, it seems.
 

Reply to boiler cross bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
829
Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP! Every so often (twice in the last two days) when running the hot...
Replies
15
Views
466
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
673
Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
888
Do you need cross bonding. Main gas and water incoming is plastic and all circuits are on RCBOs
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock