Discuss BONDING METAL WORKTOPS in the UK Electrical Forum area at ElectriciansForums.net

If It's not likely to bring in an earth from outside (extraneous) then no.
Thanks. All surfaces are metal so exposed and conductive. They could become live under fault conditions say a wire in piece of kitchen equipment was torn. So I would say yes extraneous.There are supply copper pipes in the kitchen which are bonded. Was thinking cud fit to them.
 
Thanks. All surfaces are metal so exposed and conductive. They could become live under fault conditions say a wire in piece of kitchen equipment was torn. So I would say yes extraneous.There are supply copper pipes in the kitchen which are bonded. Was thinking cud fit to them.
So could a metal chair or a knife.
 
I would say no, bonding not required.

Also, are they not movable counters, most commercial kitchens the work tops can be moved to help with cleaning down etc.
so therefore being mobile how would you attach wires to them?
 
These would most certainly NOT be extraneous conductive parts.

Unless the kitchen surfaces themselves extend externally and to the ground itself.

However I would consider them an extension of exposed conductive parts, and require supplementary bonding.

But it very much depends on circumstances, movable tables no, but if it is a complete kitchen fitted worktop with appliances resting on or adjacent to it I would add supplementary
 
These would most certainly NOT be extraneous conductive parts.

Unless the kitchen surfaces themselves extend externally and to the ground itself.

However I would consider them an extension of exposed conductive parts, and require supplementary bonding.

But it very much depends on circumstances, movable tables no, but if it is a complete kitchen fitted worktop with appliances resting on or adjacent to it I would add supplementary
Julie that is great. Getting my head around meaning of extraneous. Some of the worktops are built in and others movable but have not been moved in 20 years. There is fixed equipment on the tops. There is pipework which has good bonding. Was considering connecting to this pipework as the DB is 25m away. I did a PAT last month and the the condition of some of the equipment was awful. Failed 3 items. Not a good environment for a metal surface.
 
Julie that is great. Getting my head around meaning of extraneous. Some of the worktops are built in and others movable but have not been moved in 20 years. There is fixed equipment on the tops. There is pipework which has good bonding. Was considering connecting to this pipework as the DB is 25m away. I did a PAT last month and the the condition of some of the equipment was awful. Failed 3 items. Not a good environment for a metal surface.
Bonding is covered in 415.xx I am not sure just picking up a connection from pipework is suitable.
 
These would most certainly NOT be extraneous conductive parts.

Unless the kitchen surfaces themselves extend externally and to the ground itself.

However I would consider them an extension of exposed conductive parts, and require supplementary bonding.

But it very much depends on circumstances, movable tables no, but if it is a complete kitchen fitted worktop with appliances resting on or adjacent to it I would add supplementary
I thought an exposed conductive part would need to be earthed, not bonded.

If an exposed conductive part, it requires earthing.
Is an extraneous conductive part, it requires bonding.
If neither of the above, it requires neither earthing nor bonding
 

Reply to BONDING METAL WORKTOPS in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

If you were to test a metal staircase on the side of the house on insulation resistance and it gave you a dead short. Would that need bonding...
Replies
5
Views
344
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
863
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Hi all, it's been a while since I've been on, apologies. I am debating whether I need to replace the bonding to the gas meter. The meter is...
Replies
1
Views
334

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock