Discuss borrowed neutral in the Industrial Electricians' Talk area at ElectriciansForums.net

A

aaronstuart

Sorry for this dumb question....
What would be the easiest way of testing to see if you have a borrowed neutral?

Disconnect neutrals in cu and do a continuity test between neutrals?:confused:

My apologies in advance....
 
sorry for the short answer earlier ;with continuity you're trying to prove which circuit /s the neutral is on .

never checked your profile so i assume you know what i mean !!
 
so if you disconnect all neutrals at cu then connect on neutral of upstairs lights and neutral of downstairs lights, thats how to find it?
 
If you are concerned about a possible shared neutral to the landing light from the upstairs circuit switch off all the lighting breakers with the landing light ON.

Disconnect the downstairs live and the upstairs neutral, if you have continuity between them you have a shared neutral somewhere.
 

Reply to borrowed neutral in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
During some testing I found a N-E IR fault on the kitchen lights of 0.1Mohms. I also found a N-E IR fault on the ring sockets, again 0.1Mohms...
Replies
58
Views
8K
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
2K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
645
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...
Replies
3
Views
589

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock