today at I put 4 down lights in a bathroom, the house had been rewires 4 years ago apparently.
lights etc were on non rcd side of board, total mess, no labels, no circuit identification.
anyway, move the upstairs lights to rcd side, go up and check bedrooms, yep work fine, landing light, oh it's gone off.
i look a bit further and there's only a sodding borrowed neutral.
i stuck a big warning sticker on the CU, and put both light circuits into one breaker on the RCD side just to reduce the chances if someone getting a belt.
It's just not acceptable is it!