Discuss bs 1361 fuse in the Australia area at ElectriciansForums.net

i=p/u

-
Arms
Reaction score
801
hi ho, i just replaced replaced 8 gu10 50W bulbs in room as were blown. there is 18 on the one circuit plus 3 mini strip lights under benches very likely 18W each, they were all working when i left and when she left room she switched all 3 switches on 1 go and she said the fuse had blown, would you say by her switchen all on one go would of blown the 5A 1361 fuse ?? i personaly think to many but when you add it up its under 5 A

18 x 50W = 900W / 230V = 3.9A
3 x 18W = 54W / 230V = 0.23A so roughly 4A all in, which is under 5A

any input guys before you all go your local niteclub and dance like your up a ladder and fallling
 
u aint just a pretty dude tony are you.... when i was working there today i found half pack of 5A fuses lying on top of cu .
would you say with the fuse keep blowing would destroy the lamps aswell in some way.
 
also, it's common for the fuse to blow when a lamp fails (more so with MCBs). an anti-surge (motor rated) fuse may cure your problem though.
 
well that sounds great telectrix would they fit in to the 1361fuse carrier or am i going to have to change..., i was thinking of changiung the fuse carrier to a 15A one
 
bad idea.15A is a tad to high a rating for 1.5mm T/E . even worse if it's wired in 1.0mm. better would be to split the lighting into 2 5A circuits.
 
isnt 1.5mm rated at 18-20A or something tel. too much work involved in splitting the lighting circuit. ive told them to change to energy efficent lighting (led) just weighing up mu options for monday morning
 
New posts

Reply to bs 1361 fuse in the Australia area at ElectriciansForums.net

Similar Threads

I
A few months ago I wired a small conservatory, just the standard stuff protected by a 2 way RCD CU. At the time I was asked to quote for a re wire...
Replies
9
Views
1K
DurhamSparky
D
R
Iv been calculation voltage drop. Could some see if what im doing is correct. So from looking in the regs i have found that your aloud 6.9v...
Replies
13
Views
4K
R
My dear nan decided she wanted to upgrade her kitchen before she retires from work. She asked if if could install a few down lights and sink two...
Replies
26
Views
3K
Garythenab
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock