hi guys
after a little advice re a 30 A Type 2 BS 3871 MCB. Now i know they are old but still compliant , just checked the OSG p 49 Table 7.1 for maximum length and installation methods but there not listed.
i have the maximum ZS of 0.88 from page 103 table 2d OSG where they are listed.
can anyone advise where the allowed installation methods would be listed? or are they the same as for a type b BSEN 60898 ?
many thanks