Reaction score
834
Hi Guys

Quick one for you.
A cable that is 25M long and has a resistance of 2.3 m ohms/M ( milli ohms per metre ). A second Identical cable is to installed in parallel with this conductor. What is the total resistance of the two conductors connected in parallel?

1st conductor: 25 x 2.3 = 57.5
57.5 divided by 1000 = 0.0575

2nd conductor: 25 x 2.3 = 57.5
57.5 divided by 1000 = 0.0575

1 divided by 0.0575 + 1 divided by 0.0575 = 34.782

1 divided by 34.782 = 0.028

So 0.028 is my answer. Is this correct?:confused:

Sorry but I have no divide symbol on my computer.

Any help would be great. Got my 2391 in Jan so I am craming like mad.

Cheers

Jay
 
Looks good to me mate.


Sent from my iPhone using Tapatalk
 
hi mate
2.3 x 25 x 2 divide by 1000= 0.115ohm
is the 2.3 m/ohms per metre at 20 c if so then have to include a multiplier if 70c cable T/E multicore ie a core incorporated in a cable or bunched max temp 70c then
2.3 x 25 x 2 x 1.2 divide by 1000 = 0.138ohm or rounded up to 0.14ohm
but i may be wrong and mixing up what you are asking and someone elso more clued up may know better
 
Last edited:
hi mate
2.3 x 25 x 2 divide by 1000= 0.115ohm

Thanks for that but I think the way you have done it is if the cables where in series. Because there in parallel you have do: 1 divided by answer then 1 divided by total answer. Or so I was told when working with resistors. There was no mention of temp in the question so I guess they dont need it. Its on a past 2391 paper and I just wanted to know if I was working it out ok.

Cheers for the replys guys

Jay
 
R = (R1xR20)/(R1+R2) for resistors in parallel
 
RT = R1XR2
.......R1+ R2

as telectrix stated or when two resistances of equal resistance in parallel total resistance is half the resistance of 1 resistance.
example
R1=5 OHM R2=5 OHM
5/2 RT=2.5 OHM
 
Last edited by a moderator:
and the same rule for capacitors in series. Ct= (C1 x C2)/(C1 + C2)
 
but what about inductances in parallel, king?
 
lots of Ls and pies if i remember ( i only left colege in 2007 ) i have a terible memory, especialy formulas i would never use. If i ever need a formula i have a handy ap for my ipod, or google works just as well or if realy, realy bored i pull out my old college folders and remember how intelegent i used to be ,before jibs grading system knocked me on my bottom.
 
To remember resistances in parrallel "Divide the product by the sum"...........but for only 2 x resistances. If you have 3 x resistances use the formula for 2 x resistances then using that answer using the formula again for the 3rd resistance and so on.
 
To remember resistances in parrallel "Divide the product by the sum"...........but for only 2 x resistances. If you have 3 x resistances use the formula for 2 x resistances then using that answer using the formula again for the 3rd resistance and so on.
better way is................. 1/R = 1/R1 + 1/R2 + 1/R3 ....

eg. 3 10ohm in parallel

1/Rt = 1/10+1/10+1/10 = 3/10 : Rt = 10/3 = 3.33
 
Last edited:
hi mate
2.3 x 25 x 2 divide by 1000= 0.115ohm

Thanks for that but I think the way you have done it is if the cables where in series. Because there in parallel you have do: 1 divided by answer then 1 divided by total answer. Or so I was told when working with resistors. There was no mention of temp in the question so I guess they dont need it. Its on a past 2391 paper and I just wanted to know if I was working it out ok.

Cheers for the replys guys

Jay

Hi Jay you are correct i have worked it out for a series circuit sorry mate
I have looked into it and should have done it the way you said lol thanks for pointing my error learn something new every day mate cheers
 

Reply to Cables in parallel formula in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Replies
6
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
Replies
5
Views
2K
My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
Replies
11
Views
4K
Hello, hopefully ive got this right but if someone can check over my maths for me, id appreciate it. Im needing to install a new supply cable...
Replies
3
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock