- Reaction score
- 8,776
My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example:
If we take:
-TNCS installation with a Ze of 0.2 ohms.
-Plastic services, nothing bonded, keeping it simple
-Line conductor resistance from supply transformer should be similar to PEFC and PSCC given equal conductor sizes. So 0.2 ohms. Or is this only to nearest PME point and would be larger?
-Resistance of average human being according to google is 300 ohms
If this installation is pulling 20 amps, it can be treated basically as a resistive load of 11.5 ohms. (given nominal 230v supply)
Can I just use the voltage divider resistor formula (R2/R1+R2) to calculate voltage in the middle?
So with broken PEN and only path back being through human, R1 is 11.7 ohms, R2 is 300 ohms, so voltage at point of contact is 222v (or pretty much full supply)
And in case where someone has installed a backup earth electrode at the cut-out, with the electrode having an impedance of 50 ohms, R2 becomes 50 ohms, and the potential at the installation's exposed conductive parts is about 186v
Does that basically stack up, main variables being:
-resistance of earth, resistance at humans feet etc.
-current draw of installation
-impedance of earth rod
-resistance of line and cpc conductors within installation (completely omitted above)
Would parallel paths to earth via bonded services be calculated by 1/R=(1/R2) + (1/R2) + (1/Rn) and substitute that value for R2?
Thank you to anyone who got to the end and is willing to comment!
If we take:
-TNCS installation with a Ze of 0.2 ohms.
-Plastic services, nothing bonded, keeping it simple
-Line conductor resistance from supply transformer should be similar to PEFC and PSCC given equal conductor sizes. So 0.2 ohms. Or is this only to nearest PME point and would be larger?
-Resistance of average human being according to google is 300 ohms
If this installation is pulling 20 amps, it can be treated basically as a resistive load of 11.5 ohms. (given nominal 230v supply)
Can I just use the voltage divider resistor formula (R2/R1+R2) to calculate voltage in the middle?
So with broken PEN and only path back being through human, R1 is 11.7 ohms, R2 is 300 ohms, so voltage at point of contact is 222v (or pretty much full supply)
And in case where someone has installed a backup earth electrode at the cut-out, with the electrode having an impedance of 50 ohms, R2 becomes 50 ohms, and the potential at the installation's exposed conductive parts is about 186v
Does that basically stack up, main variables being:
-resistance of earth, resistance at humans feet etc.
-current draw of installation
-impedance of earth rod
-resistance of line and cpc conductors within installation (completely omitted above)
Would parallel paths to earth via bonded services be calculated by 1/R=(1/R2) + (1/R2) + (1/Rn) and substitute that value for R2?
Thank you to anyone who got to the end and is willing to comment!