Discuss can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW shower in the UK Electrical Forum area at ElectriciansForums.net

Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Mate you can't put the cables on separate MCB's end off. You need to read the part in bs7671 regarding conductors in parallel.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

But the (40A) current is shared down two 6mm cables (approx 20A down each). And each 6mm cable has its own 30A mcb back in the CU. From the 50A isolator pull switch near shower, where they join, the single cable to the shower is then 10mm. I cant see any over loading / overheating at all. Am I still missing something here.

Except for failure to comply with regulations why would this not be safe?
Any advice really appreciated
Thanks
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

perfectly OK till the insulation monkeys smother the cable.

I agree, but should we have to comply with every idiot that might come along and do something like this. The insulation monkeys should be educated, before stuffing the loft full of the stuff!

EDIT: Just read this again, I don't think you was implying we should :oops:
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

But the (40A) current is shared down two 6mm cables (approx 20A down each). And each 6mm cable has its own 30A mcb back in the CU. From the 50A isolator pull switch near shower, where they join, the single cable to the shower is then 10mm. I cant see any over loading / overheating at all. Am I still missing something here.

Except for failure to comply with regulations why would this not be safe?
Any advice really appreciated
Thanks

If you think a 30A mcb will trip out at 30A you are mistaken.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

But the (40A) current is shared down two 6mm cables (approx 20A down each). And each 6mm cable has its own 30A mcb back in the CU. From the 50A isolator pull switch near shower, where they join, the single cable to the shower is then 10mm. I cant see any over loading / overheating at all. Am I still missing something here.

Except for failure to comply with regulations why would this not be safe?
Any advice really appreciated
Thanks

What training/competence/test kit do you have?
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Op can I ask your qualifications please as this is basic stuff.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

I just think we need to leave this thread alone, no matter what we tell the OP it just seems to fall on deaf ears.

I want to know who is going to get here first Glenn or Biff.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

This thread is the classic example of how Dan needs to change the forum. If the OP is unwilling to attempt to answer some of the questions he should be put on a ban until he does.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

According to his profile he's a teacher, hope he knows a bloody sight more about that than he does about electrics .
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

But the (40A) current is shared down two 6mm cables (approx 20A down each). And each 6mm cable has its own 30A mcb back in the CU. From the 50A isolator pull switch near shower, where they join, the single cable to the shower is then 10mm. I cant see any over loading / overheating at all. Am I still missing something here.

Except for failure to comply with regulations why would this not be safe?
Any advice really appreciated
Thanks
OK buddy. Jokes over. You've had your fun now toddle off to some other trades website and wind them up
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

My god, i didn't realise until half way through he was talking about two seperate breakers bahahahahah. This has to be a wind up.

Jim
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

theres only 1 poster i can think of that covers this........


GFP.png
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

This thread is the classic example of how Dan needs to change the forum. If the OP is unwilling to attempt to answer some of the questions he should be put on a ban until he does.

Unfortunately this will not stop him doing what he thinks is OK.

Any basic understanding of the regs tells you this can't be done.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Thanks to you who have replied genuinely to my question, without feeling the need to result to sarcasm. No I am not a qualified electrician and never claimed to be but I am both a physics graduate and electronics engineer. I never doubted that regs would not allow this to be done, though from an electrical theory perspective it is perfectly feasible, Its a shame very few replies seemed to go beyond 'you cant do it as it breaks the regs' and considered the theoretical reasons why...of which there are few.
Thanks again
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

replace individual mcb for each cable for 1x mcb for both cables. 32a should do the job. connect both cables to it, then join them at other end and attach to a length of 10mm going into the shower.
 
Re: can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW sh

Thanks to you who have replied genuinely to my question, without feeling the need to result to sarcasm. No I am not a qualified electrician and never claimed to be but I am both a physics graduate and electronics engineer. I never doubted that regs would not allow this to be done, though from an electrical theory perspective it is perfectly feasible, Its a shame very few replies seemed to go beyond 'you cant do it as it breaks the regs' and considered the theoretical reasons why...of which there are few.
Thanks again

The main reason being that supplying a circuit with two separate MCB's creates problems with isolation. Another reason is that two MCB's in parallel are an unknown quantity for short circuit and overload protection. You cant do it. End of.
 

Reply to can two 6mm csa cables each with 30A mcb in joined at 50A dps to supply 9.5kW shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I’m new to this forum so please bear with me. I live in a bungalow and would like to repurpose an unused shower cable to supply one new...
Replies
0
Views
4K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
Some time ago I built a toilet and shower area at the end of my detached garage for use when doing outside DIY or gardening jobs instead of...
Replies
26
Views
7K
Hi guys, I am running a supply to an outbuilding that requires a 22m run from the Main CU (in the garage) to the CU in the outbuilding, at the...
Replies
55
Views
10K
Hello folks, I've just visited the retirement flat of an elderly couple who want RCD protection added to all of their circuits. Yes,all of...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock