Discuss Can’t find rcbo for this unit in the UK Electrical Forum area at ElectriciansForums.net

Baddegg

-
Esteemed
Arms
Supporter
Patron
Reaction score
5,397
Anyone know where I can get some rcbo a for this? Tried the wholesalers locally but no luck,
8E59F455-1A00-403C-B957-9DD61F70641D.png
 
I need to fit new shower unit and the manufacturer states it needs to be protected by its own rcd,if I’ve read it right,would 40amo mcb and the existing 30ma main switch suffice?
 
Not 100% sure they are compatible for the Series E but if they are that CU has quite a restricted height. As Andy says the true Series E were two module.
 
If you are going to attempt to fit an rcbo in that board you still have the rcd main switch and hence you have no selectivity (new 18th Ed word:D). You may as well fit an mcb and use the rcd of the main switch, fitting a 40A rcbo which may not be compatible along with 10.0 cable, assuming this is the size you will use will be a mare to fit into that board.
 
I need to fit new shower unit and the manufacturer states it needs to be protected by its own rcd,if I’ve read it right,would 40amo mcb and the existing 30ma main switch suffice?

Hum .... Why do you need a rcbo if the board already has this protection in place?

If you aren't convinced ring your scheme?
 
Thanks for all the advice,believe it or not cef own brand MCG do fit in but yes very tight,I’m not a fan of mix n matching brands,thanks telectrix I think I’m going to recommend a new board.
Haven’t seen any of the 18th yet westward,selectivity?
 
so now I'm not discriminatory to other trades, I' m selective. does that mean i can select which goes into the electric chair first, wet-pants or muck spreader?
 

Reply to Can’t find rcbo for this unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Folks. I need to install a defib unit outside on a wall. Does this require an RCBO or not, just wondering as the unit has a small heater within...
Replies
15
Views
529
Hello everyone, Is it necessary to test RCBO x5? Some say that you can’t even test at x5 times because it can damage RCBO. Others that you can...
Replies
4
Views
906
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
772
Hi got a 8 panel solar system on bungalow, changing the board to 18th edition spd board Solar feed is chased into wall so will this need a type B...
Replies
4
Views
265
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock