Buzz-light-bulb

Does anyone know anywhere in the regulations that it states I have to use capping to protect cables when embedded in plaster as I am currently on a rewire, it says in on site guide that if there's no rcd protection it does require metal earthed capping
 
nothing wrong with that chase. it's the wide-angle lens makes everything look pi$$ed. ask tony. he's a photography expert.
 
one of the reasons i use capping is it is possible to replace the cables after how many rewires have you done when you can pull the old wire out and replace them ,did one a few weeks ago guy had drilled through the cable and bodged the repair was able to pull out the damaged cables and replace them , you cant do that if they are plastered in , it was either chase the full wall out or a 3 inch round patch , when you look at costs , half hour to replace the cables completely down the wall or 2 hours to chase and patch redecorate
 
As for the cost ! It adds pence to a run when using oval conduit .
If installed correctly , it is perfectly accessible when it comes to replacing , even pulling the odd extra cable down when needed .
It looks 100% more professional to the client than just clipping direct , no matter how neat your clipping is , and a damn site quicker .
The above does depend on if the chase has been cut with a decent wall chaser ( but then again if you have not got this or the extract gear to go with it , I pity any other trades working along side you on a rewire ! ) .
I know it is purely down to choice , but it is a no brainer as I see it .
 
We use sto25 , and all you do place it in the chase when you have fed the cables in ( straight and not twisted) tight up to one side , mark your fixing points normally between two or three for the length drill , plug and fix leaving the screw heads just above the conduit . You will find that it is quite easy and a perfectly sturdy fixing until the spreader comes along , and if the mortar is soft enough , you are able to fix straight in to it , as it is only going to be a temporary fixing for a few days until spread .
 
https://www.google.co.uk/search?q=O...XY7Aa-zYG4Bw&ved=0CAkQ_AUoAQ&biw=1024&bih=660

More tubing good points...
Let a 'Monkey' (for want of a better word!) fit all your tubing, plasterer makes good.
You come along later, pull cables in, test and finish off etc., knowing full well there's no damage whatsoever to your wiring.
And it improves the Maintainability of the install.

Capping is history, the future is Oval tube, and the future is (has been) here and now!
 

Reply to capping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock