Discuss Caravan Hook-Up RCBO Current Rating in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have a small caravan park with 8 pitches. Each have a Rolec Electrical Hook-Up unit fitted with a Rolec 16A Single Pole and Neutral 2 Module C Curve 6kA 30mA RCBO.

I've recently fitted meters to these units which display voltage, Current and kW. I was surprised to see that some of the caravans were displaying currents over 20A and the 16A RCBO still had not tripped. I checked this myself with a 5kW load on all 8 units and not one of the 16A RCBO's tripped.

Should these RCBO's not trip if the current goes over the rated16A?
 
As above, the MCB is designed to have a thermal overload protection curve to match a cable, so a small overload for a long time, or a large overload for a short time, is needed to trip it.

Then they have a 'fault' trip where the magnetic part kicks in and for a C-curve MCB that is between 5 and 10 times its rating (so your 16A C device would go in tens of milliseconds or less at 80-160A fault).

Finally the RCD side of the RCBO is designed to trip on an imbalance of current that is between 0.5 and 1 times its rating, so the typical 30mA sort used for most final circuits will not trip below 15mA, might trip for 15-30mA and should always trip above 30mA.
 
The age old question…. What are people doing in their caravans to generate anything near 16A?

We had statics where the owners had about 6 or 7 different electric heaters, and wondered why the electric tripped.
My answer was always….. “why have you got electric heaters in a gas powered centrally heated van?”
 
Thanks. That explains for the extra power consumption I wasn't expecting over the winter. Some caravans seem to be drawing more than 16A over 24 hours which meant that with our pitch price, which was inclusive of electricity back then, we were running at a loss!
I've now installed smart meters but they limit the supply to 20A and then shut down. Unfortunately the customers can't reset these themselves so I'm getting calls all day and night. I need the RCBO to trip before the supply hits 20A. Any ideas?
 
Thanks. That explains for the extra power consumption I wasn't expecting over the winter. Some caravans seem to be drawing more than 16A over 24 hours which meant that with our pitch price, which was inclusive of electricity back then, we were running at a loss!
Yes, recently that would be a real penalty.
I've now installed smart meters but they limit the supply to 20A and then shut down. Unfortunately the customers can't reset these themselves so I'm getting calls all day and night. I need the RCBO to trip before the supply hits 20A. Any ideas?
Fit a 10A RCBO C-curve. That will cope with a 2kW heater and light electronics use, or a 3kW / 13A kettle for enough time to boil the water, etc.

If you need lower average but a bit more switch-on surge protection you don't get D-curve RCBO but you can use a D-curve MCB and separate RCD, if there is space for it.
 
As an aside, the fancy electronic-trip MCCB allow you to adjust the trip curve in many ways to get the characteristics you want, but they are seriously expensive (usually not much change from £1000) and targeted at much larger system.
 
Running a 16A breaker overload for an extended time period can damage it.

Now the hook ups are metered…. Charge them per unit… then see how much they use. I bet they’ll reduce consumption.

(Check. I don’t think you can charge per unit any higher than you pay from your supplier)
 
(Check. I don’t think you can charge per unit any higher than you pay from your supplier)
I was wondering about that, and if that applies everywhere or just for a BNO/landlord powering flats, etc?

At my work we are going to have another metal cabin for a client on site and were proposing to charge electricity as 5% above our rate based on the meter for them to allow for the losses in the sub-main, etc, feeding the site as our landlord meters at the busbar chamber end. But that is more a commercial lease sort of deal and maybe very different.
 

Reply to Caravan Hook-Up RCBO Current Rating in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I'm sure this will have been covered before but please bear with me. Have been asked to replace a main Distribution board for a fairly small...
Replies
23
Views
5K
Hi all So had some issues lately related to high current fittings .. dp switches mostly. A number of electric boilers of various ratings .. from...
Replies
24
Views
2K
Hi all, First time post to the forums, I hope you all go easy on me! We are undertaking an electrical install as apart of a solar PV...
Replies
5
Views
981

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock