Double insulated cable is slightly misleading term although not exactly incorrect. The insulation surrounds the conductor directly, the sheath is the environmental protection and yes it has insulating qualities that may match the actual insulation itself but is also will be design to cope with the expected environmental conditions to which it is normally installed.

I use specialised cables a lot in machinery and the sheath of which there may be several layers are all designed to ensure the insulation is protected and maintained and is not subject to anything that may break it down.

You are not technically incorrect to use the term double insulated as that is one of its attributes but if you were to do my job then that term would not suffice and they would be clueless to which cable I wanted.
The way I understand it and a square within a square symbol details is what I have said above. I get what you’re saying though. I was just stating that the outside sheathed is not insulation.
 
The way I understand it and a square within a square symbol details is what I have said above. I get what you’re saying though. I was just stating that the outside sheathed is not insulation.

Don't forget double insulation requirements can also be satisfied by one layer of 'reinforced ' material.
 
Class I and class II (we shouldn't really use 1 or 2) can only refer to the product / appliance not the cable. As stated above cable does not actually comply as class II, even though it may indeed have two independent layers of insulation.

The current approach is to protect for a single fault, that's the whole principle of the wiring regulations, and pretty much all other associated standards - IEC 61140 included.

Thus class I if the insulation fails, it uses ads - there is no further faults considered, as a product you don't supply additional earthing arrangements etc to cover the case that the cpc isn't connected.

Similarly class II if the insulation fails, it is a second layer of insulation (or reinforced) - no further faults are considered.

If the cable enters a class II product without sufficient protection to ensure compliance with class II, then it is a poorly made product, or not compliant at all i.e. a cheap knock-off - it doesn't mean that the principles of product classes is incorrect
 

Reply to Class 2 product? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top