Any ideas how to bend 70mm swa cable round a corner brick wall.
It’s gotta look good,cable not yet ready to cleat,but looking at the route the only problem I see is this corner,especially with the radius bend-of the cable,just wondering how you guys would overcome it.
 
You could dress it around with this
upload_2018-6-20_18-39-58.jpeg
 
Actually if it’s not in the way could you not put it on tray? If it’s only 3 core it’s about 35mm OD so it’s bending radius would be about 250mm. If the tray came in tight on the corner of the building you would only need to stand the rest of it off of the building by 75mm to get that radius.
This is only rough workings though.
 
Actually if it’s not in the way could you not put it on tray? If it’s only 3 core it’s about 35mm OD so it’s bending radius would be about 250mm. If the tray came in tight on the corner of the building you would only need to stand the rest of it off of the building by 75mm to get that radius.
This is only rough workings though.
Sounds good
 

Reply to Cleating or cable tray 70mm 4 core swa in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
447
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Hi All, I’m after some advice. I’ll cut to the chase but I can give more detail if needed. A 400A sub main supply needs to be ran 100m, a pretty...
Replies
5
Views
2K
Looking for some advice; I am intending to mount two led downlights on pillars/brick walls either side of the garage door opening. I will drill...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock