DBs located in every room.
7 x circuits in All DBs.
Im doing condition reports.
Many of the DBs have been installed as the pic attached. The top surface of the DB has been completely removed andbbutted up to ceiling. A large hole in the plasterboard with cables entering. No gland on the SWA feed also entering through the plasterboard.
C2s
-No swa gland
-fire barrier not made good where cables pass through ceiling.
- dust ingress entering from ceiling void due to method of installation.
-integrity of DB not maintained due to removal of top surface.

Other rooms have DBs mounted in cupboard. A large bush in top surface for cable entry and is mounted high level. Ip4x not maintained but only accessible via step ladder. Live parts potentially accessible, can get finger through but very unlikely.

C2
Mini fridge socket in every room has no rcd protection and is not labelled for specific use. Also the caretaker has mentioned its often unplugged and used by guests for other things. Another point alrough very unlike again on ground floor there is patio doors in all rooms, potential for use outdoors in a hotel room would you take this into consideration?

Thats enough for now. Plenty more obs for such a new installation.
 

Reply to Coding eicr in 11 year old hotel. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
565
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
384
Just wanted to get some thoughts from other electricians who regularly do EICRS, does anyone else code a fan isolater with no 3A fuse protection?
Replies
23
Views
927
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
521

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock