Discuss commercial dsitribution board change leaving existing circuits non rcd protected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

H

hodgey1972

I am changing a commercial distribution board like for like, Can someone confirm im correct?
Ive only allowed rcd (rcbo) protection for new circuits or circuits im working on, and noting in my installation cert, that those existing lighting circuits don't comply with amendment 3 regarding rcd protection.
Or where i should be looking in 7671 or to quote from
Thanks in advance.
 
Last edited by a moderator:
Would have thought that considering you are changing the complete Distribution board, including connecting your new circuits and the existing ones, the consideration should be given to protecting the existing circuits as well as the new ones.
After all you will be certifying the whole board and taking responsibility for the complete installation. Perhaps an EICR would nave been a better option, reporting your findings rather than just noting the omissions on the certificate. My opinion only.
 
Any additions or alterations should comply with the current regulations.
You are changing the DB and altering the OCPD for each circuit and altering the characteristics of the circuit.
If the lighting circuits require 30mA RCD protection it should be provided.
 
This depends on the reason for a new distribution, if you are simply replacing like for like as you state but just a larger board then you effectively haven't changed any characteristics of the existing circuit and confirmation tests to their condition plus a note on the cert' would be all I would do. This is common if you wish to re-use all the existing OCPD's to save money when simply increasing the board size.
 
To start with, any Certification issued should show the extent of the work.
Unless you particularly want to, there is nothing which makes you responsible for any part of the existing installation.
Secondly, there is nothing in BS7671 which refers to changing a circuit's characteristics, or suggesting that because of any such change, the circuit should be treated as being new.
As far as I am aware, there is no new requirement in Amendment 3 for lighting circuits to be provided with RCD protection?
 
Rcd protection for buried cables in this case wall lights and switches
There is no new requirement for buried cables to be provided with RCD protection in Amendment 3.
In fact there is no requirement in BS7671 for buried cables to be provided with RCD protection, it is just one of a number of options available. However not an acceptable method fo rambles run beneath floors or above ceilings.
 
Also if I'm correct is there anything in bs7671 or eawa I can use in my defence of my decision? I have a demanding client who I know thinks they will be able to try and push liability for the whole installation towards me, after reducing my quote for re-wiring to not include said circuits
 
The EAWA requires that anyone who's work activities require experience, knowledge or sufficient supervision to safeguard against the dangers electricity may present, should be provided with such.
It is not your responsibility to ensure employes of the company you are carrying out the work for are suitably experienced, trained or supervised.
However there is now a requirement in BS7671 which requires RCD protection be installed unless there is a documented Risk Assessment indicating such RCD protection is not necessary.
It is the responsibility of your client to produce such a Risk Assessment.
 
I would argue that in the case of a board change where the OCPD is changed then as long as you have not made the circuit any less safe then you can treat it still as an existing circuit wired to a previous edition of the regulations, I cannot see why changing a board should make you bring any circuit up to standards just because the OCPD has different characteristics, as long as the circuit isn't a code 1 for any reason then I would treat as existing.

This is my opinion not a regulation, I believe you have to ensure that any alteration or edition must comply to current regulations where this is in the form of altering or adding to the circuit then yes! your work should follow current regulation but where the alteration is not the circuit but the actual device protecting the circuit then as long as it doesn't afford any less protection for the circuit than the previous device it should be the case you don't have to bring the whole circuit up to regulations.
 
Last edited:
I would argue that in the case of a board change where the OCPD is changed then as long as you have not made the circuit any less safe then you can treat it still as an existing circuit wired to a previous edition of the regulations, I cannot see why changing a board should make you bring any circuit up to standards just because the OCPD has different characteristics, as long as the circuit isn't a code 1 for any reason then I would treat as existing.

This is my opinion not a regulation, I believe you have to ensure that any alteration or edition must comply to current regulations where this is in the form of altering or adding to the circuit then yes! your work should follow current regulation but where the alteration is not the circuit but the actual device protecting the circuit then as long as it doesn't afford any less protection for the circuit than the previous device it should be the case you don't have to bring the whole circuit up to regulations.

not sure if i have misunderstood here..

by changing the fuse board- you work has to comply to the current regs- so if existing circuits require rcd protection- then you must protect them by rcd

you can't just change to a 16ed fuse board and then only rcbo a new circuit you have installed!

or am I reading wrong here lol
 
not sure if i have misunderstood here..

by changing the fuse board- you work has to comply to the current regs- so if existing circuits require rcd protection- then you must protect them by rcd

you can't just change to a 16ed fuse board and then only rcbo a new circuit you have installed!

or am I reading wrong here lol

Its an opinion hence I stated it, but on that note where in the regs does it say that, this is down to interpretation IMHO, you are changing the board, the board itself must be within regulations and I would argue that because you are not making any alteration or additions to the actual circuit and you don't leave it any worse off than before you started and as long as you test it is safe to re-energise then you do not have to bring it up to 17th edition, think about it most of the circuits probably contravene more than just requiring RCD cover so in effect your just addressing and updating one point and not others...

I too was pulled into that way of thinking but questioned where it came from and where are the regulations to state that, you are not altering the circuit in anyway you are exchanging the OCPD that monitors the circuit which will give the same protection as before if not more.

I'm not against adding rcd protection where you can but just expressing IMHO its not a requirement.
 
The requirement, is that your work must comply with BS7671.
There is no requirement for you to upgrade existing circuits.
Also there is only a requirement for certain circuits to be provided RCD protection, such circuits as those of a location, containing a bath or shower or socket circuits in agricultural/horticultural installations.
 
The requirement, is that your work must comply with BS7671.
There is no requirement for you to upgrade existing circuits.
Also there is only a requirement for certain circuits to be provided RCD protection, such circuits as those of a location, containing a bath or shower or socket circuits in agricultural/horticultural installations.

and the others...
 

Reply to commercial dsitribution board change leaving existing circuits non rcd protected in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

As I've mainly done site work and moved into domestic recently, I'm a bit rusty on stuff like this, but if I'm adding a loft PIV unit to an...
Replies
1
Views
637
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
983
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
675
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock