Search the forum,

Discuss connection of pv system onto split phase supply. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

P

paulsamuel1984

Hi,

Has anyone had any experience connecting PV onto a split phase supply?

Should I be balancing single phase inverters to supply each phase? 3 phase inverters are a no go?

Any help would be greatly appreciated.

Thanks Paul
 
Thanks for the info. That is very useful!!

Presumably I can use single phase inverters as long as a balance the phases if I wished to do so, although I think I will now go with the Fronius.

The Client was looking for a large installation to cover a barn, which I suggested was not feasible on split phase system, DNO agreed with this as they estimated £50-£75k to upgrade to a 3ph system.

Thanks,

Paul
 
Did an install on a split phase system but was <4kw I was advised by the DNO to keep it under 3.7kw as this is the allowable inbalance between phases ,he also said that to go >4kw would definitely involve reinforcement costs
one inverter <3.7kw on one phase should'nt be a problem, two the same size on two phases also ok
 

Reply to connection of pv system onto split phase supply. in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

hi A property with split phase. 0 degrees apart. there is an existing 3.6kw system on the phase. Thinking about installing an additional 3.6kw...
Replies
0
Views
834
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
336
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
25
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top