- Reaction score
- 2,089
Posted while I was writingSee #38. Is said cupboard providing an EFFECTIVE barrier.
Discuss Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net
Posted while I was writingSee #38. Is said cupboard providing an EFFECTIVE barrier.
701.32.1 ........................doors, floors and fixed partitions may be taken into account where these EFECTIVELY limit the extent of locations containing a bath or shower as well as their zones.
And see #10 ;-)See #38. Is said cupboard providing an EFFECTIVE barrier.
A cupboard isn't listed as something that can be taken into account to limit a zone, and it says a door has to "effectively" limit the extents of the zones and I'd argue this one doesn't.
THis...Rules and regs dont make a lot of sense at times . For me this install is a Joke and a mockery of what is safe etc . That telephone shower hose can easily reach and spray water directly onto the cupboard .lets see if anyone happy with the regs would let their child take a shower in this bathroom !It doesn't. But an electric shower mounted in zone 1 is only correctly IP rated for the zone if the cover has not been removed. The cover of an electric shower can only be removed by use of a tool. Same principal could be applied to any item of electrical equipment, if one was desperate to make it comply.
I'm just playing devil's advocate here, there's no way I would want a consumer unit anywhere in a bathroom.
I think most would agree that the situation is far from ideal and I doubt many, if any would commission such an installation.
Maybe something like this would be acceptable?
IP66 MCB Distribution Boards | Blakley Electrics
Heavy duty Single and Three-Phase IP66 MCB Distribution Boards for installation in extremely wet or very dusty locations.www.blakley.co.uk
Agreed. While having it locked is (in some ways) an improvement, there are still issues, in particular that locking it impairs isolating power quickly or restoring power (e.g. lights) quickly.Although a keyed lock could easily be fitted to the cupboard door, the suitability of the equipment is not good for the environment.
But then that brings up the accessibility of the CU and inconvienence caused to reset a tripped breakerThe cheapest solution is to box it in the cupboard, it's then out of zones and out of reach. It would just be a C3 for access but a bit of a bodge. The ideal and recommended solution is to relocate it.
I was thinking similar someone in the shower and another person knocks on the bathroom door asking the person in the shower to reset a tripped breakerDaft scenario: someone's alone in the house, having a bath, and the lights trip. Standing in a foot of water in a slippy bath, dripping wet, scrambling for a key to operate a breaker doesn't seem a very acceptable scenario!
Or relocate the bathroom!!. Why create work for the electrician because the plumber or more likely the not so handy handyman screwed upThe only solution I'd be happy with is putting the whole lot in an IP box or two and extending supply and final circuits to somewhere else.
Reply to Consumer unit in bathroom in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.