Discuss ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

A “ Circuit “ conformsto a Design . Example :

The Job am on . Wants RCBOs – Only :svengo:

O.S.G. . p/19
Type of Protective Device .
The Consumer Unit ( or DistributionBoard ) ( DB ) containsdevices for the Protection of the Final Circuit . AGAINST

i) Overload - 433.Regulations .
ii) Short – Circuit -434. Regulations .
iii) Earth Fault . 434. Regulations.

Function (i) & (ii) are carried out usually by One Device . Circuit Breaker .
Function (iii) may beCarried out by the CircuitBreaker provided for function (i) & (ii) . or by an RCD .

An RCBO . being a Combined – Circuit Breaker& RCD . Will carry out Functions .(i) – (ii) & (iii) ◄◄ :hurray:

Conforms to a Design . BritishStandards – 2008 :20:

 
2392-10 : some Revision . :icon_bs:

Prospective Fault Current ( PFC ) is the ►►Highest of the ►► ( PEFC ) & ( PSCC ) ◄◄
it is the Greater of these Two . Prospective Fault Currents . :uhoh2:

Remember the Difference in wording between ( Guidance ) & ( Regulation ) :dots:

O.S.G. 10.2.2. – States . That with the Supply Connected .
i) Check polarity withthe Supply Connected . Using an approved voltage indicator .
ii) Earth Electrode résistanceusing a Loop Impedance tester
GN-3 . p/48 .
Switch OFF Supply before Disconnecting the Earth .
A Loop Impedance tester is connected between the Line conductor at the Source of the TT Installation & the Earth Electrode . & a test performed . The Impedancereading taken is Treated as the Earth Electrode résistance BS-7671:2008 . Ra - I∆n ≤ 50V.
iii) Earth Fault Loop Impedance .
i) GN-3 . p/49 . Toverify that there is an Earth Connection .

iv) Prospective Fault Current Measurement . if not determined by Enquiry of the Distributor .
Prospective Fault Current ( PFC ) is the ►►Highest of the ►► ( PEFC ) & ( PSCC ) ◄◄

GN-3 . p/52
Prospective Fault Current .
Regulation 612.11. requires that the Prospective Fault Current (Ipf ) under both Short-Circuit & Earth Fault Conditions . be Measured . Calculatedor Determined by another method . At the Origin & at other relevant pointsin the Installation .

GN-3 . 434.5.1. States that the Breaking capacity rating of Each Protective Device shallbe NOT Less than the Prospective Fault Currentat its point of Installation
The “ TERMProspective Fault Current “ includes the Prospective Short-Circuit Current & the Prospective Earth Fault Current . it is the Greater ofthese Two Prospective Fault Currents . Which should be Determined & Compared with the breaking capacity of the Device .

v) Functional Testing . including RCDs & Switchgear

-&-s : 2392-10 .
As Testers . Sorry “ Inspectors
On a NEW Installation you Must Not Carry Out Live Tests until you have ( Verified ◄◄ ) the Earth Continuity ◄◄ & Other Dead Tests – “ Polarity “
 
Chapter 61 : p/155 .2392-10

Initial Verification . ( Inspection & Testing ) Two different Words . :icon_bs:

611 – Inspection .
612 – Testing .
 
2392-10 . ( T ) Some times when you see it written . You get a better Picture . Yeah . Amber . :icon_bs: :uhoh2:


610.1. Every Installation shall . during its Erection& on Completion before beingput into Service . be Inspected & Tested to Verify . as far as is reasonably Practicable . that the requirementsof the Regulations have been met .

610.2. Sections . 131 .311 to 313 & 514.9.1. ( for information required for a Fundament Principles )
610.3. The Verification shall include comparison of the “ Results “ with the relevant criteria to Confirm that therequirements of the Regulations have been Met .
610.4. For an Addition orAlteration to an Existing Installation . it shall be Verified that the Addition or Alteration complies with the Regulations .& does not Impair the Safety of the Existing Installation .

610.5 – The Verification shall be Made by A Competent Person .
610.6. On Completion ofthe Verification .According to Regulations . 610.1. to 610.5. a Certificate orCertificates . shall be Prepared .

Section 611 – Inspection :
611.1. – The Inspection shall procedure Testing & shallnormally done with that part of the InstallationUnder Inspection . ( Disconnected ◄◄ ) from theSupply .

611.2. – The Inspection shall be made to Verify that theInstalled Electrical Equipment is .
In Compliance withSection 511 – This may be Ascertained byMark or be Certification furnished bythe Installer or by the Manufacturer ) &

Correctly selected & erected in Accordance with theRegulations . &

Not Visibly damaged orDefective . so as to Impair Safety .

612 – Testing : ▼▼
The tests of the Regulation 612.2. to 612.13 . Where relevant . Shall be carried Out & theresults compared with the relevant criteria .

612 – Testing : ▼▼ PAGE– 157 . -&-s big time
The tests of Regulation 612.2. to 612.6. . Where relevantshall be carried Out ( in that Order ◄◄ ) before TheInstallation is Energised .

Where the Installation incorporates an Earth Electrode . Thetest of Regulation 612.7. shall also becarried out ( Before ◄◄ ) TheInstallation is Energised .

612 – Testing : ▼▼ PAGE– 157 . -&-s big time .
If any Test Indicates aFailure to comply . that Test . & any preceding tests . The results of whichmay have been Influenced by the Fault has been Rectified .


Chapsplease hit the Thank you Button . I don’t know if you want any more of thisStuff . ???????????? Amber :dots:


 

What the Regulations Requires -

612.12. Check of Phase Sequence .
For Multi – Phase circuits there is a Requirement to ( Verify ) ThatPhase Sequence is ( Maintained ) :icon_bs:
 
2392-10 : We use this Dayin Day out . Yeah . “ ConsumerUnit “ :icon_bs:
Section 514 : Identification& Notices .

514.8. – Identification of the Protective Device .
Circuit Protective Devices are required to be Arranged & Identifiedso that the Circuit Protected may be Easily Recognised .

 
Workingmy why around 17[SUP]th[/SUP] Edition :hurray:

Making you Aware .

538.4. Residual Current Monitor ( RCM )

An– RCM permanently monitors any leakage current . in the downstreamInstallation or part of it . such a device is NOT intended to provide protection against Electric Shock

538.4.1.
InSupply Systems . RCMs may be installed toreduced the risk of operation of the protective device in the event of excessiveleakage current of the Installation or the connected appliances .

The RCM is intended toalert the User of the Installation before the protective device isactivated .

Wherean RCM is installed Upstream of the RCM . it is recommended that the RCM has arated residual operating current . NOT EXCEEDINGa THIRD of that of the RCD


 
Short Circuit :- Two or more Live conductors touching each other . :svengo:

Evaluation of Thermal Constraints .
Fault current ( I )is found from .

( I ) = Uo / Zs .

Where:
Uo = nominal Line voltageto Earth .
Zs = Calculated value of Loop Impedance .

( I ) = 230 ÷ 0.53 = 434A
 
Part1 : Fundamental Principles . :6:

Regulation– 132.13 . Documentation for the Electrical Installation.
Requiresthat documentation . required by regulation – 514.9. & part 6 . isprovided for Every Electrical Installation .

Regulation– 134.1.1. Erection & InitialVerification of Electrical Installations .
Requiresthat good workmanship shall beundertaken by Competent Persons & further requires the “ ManufacturesInstructions shall be followed . Etc .

 
Apprentices: 612 - Testing . Red Book – 2008

Terequired Tests to be for “ Initial VerificationNew /Installation .
Thetests should be carried out in a prescribed Sequence . Some prior to the Circuits being “ Energized

Tests– Prior tothe installation being “ Energized “ Dead / Testing :6:
612.2.- Continuity of protective conductors .
612.2.2.- Continuity of rind final circuit conductors .
612.3.- Insulation résistance – ( IR )
612.4.- Protection by SELV . PELV . or by electricalseparation
612.4.5.- Basic protection by a barrier or an enclosureprovided during erection . IP2X or IPXXB .or IP4X or IPXXD .
612.5.- Insulation résistance / impedance of floors & walls .
612.6.- Polarity .
612.7.- Earth electrode .

Testsfollowing the Installation being “ Energized “ :6:
612.9.- Protection by AutomaticDisconnection of the Supply- Earth Fault LoopImpedance .
612.10.- Additional protection ( RCDs )
612.11.– Prospective faultcurrent . ( PFC )
612.12.– Check of Phase sequence .
612.13.– Functional testing . – 2392-10 . LastTest to do .
612.14.– Verification of voltage drop . 2392-10- Verification of voltage drop is not normally required during Initial Verification . New / Installation .


 
Chapter 526 . p/106

Electrical Connections .

526.1 – For every connectionbetween conductors . or between conductor & other equipment shall provide durableelectrical continuity & adequate mechanical strength & provide protection .
 
Chapter 529 -
Selection& Erection of Wiring System in relation to Maintainability . Including Cleaning . :6:

Threeset of regulations in this section .

529.1– is not Used .
529.2. & 529.3.
 
Industrial Inspection& Test – Initial Verification :vanish:

EarthLoop Impedance .

( Ze ) = 0.04Ω
TheEarth Fault Loop Impedance ( Zs ) = 0.43Ω

TheEarth Loop Impedance can be calculated before making the equipment live . by adding the ( R1 + R2 ) to the Earth Loop Impedance to the point of Supply .
This would satisfy the First requirement of Regulation 14 –Electricity at Work Regulation 1989 .

Which Requires “ There must be good reason for thecircuits to be ( Live ) whilst work is carried out on them .

Working On or Near Live Conductors .
Regulation 14 – Noperson shall be engaged in any work activity on or near any ( Live Conductor) other than one suitably covered with Insulating Material so as to preventDanger . That Danger may arise unless .

a)it is unreasonable in all the circumstances for it to be Dead . &
b)it is reasonable in all the circumstances for him to be at work on or near itwhile it is Live . &
c)suitable precautions ( including where necessary the provision of suitableprotective equipment ) are taken to prevent Injury.

Sanctionfor ( Live ) Functional Checking .

Thesatisfy regulation 14 – You have . Sound SafeSystem of Work
Onlymake circuits ( Live ) wherenecessary . for the Testing . making sure which is Live & which isDead .

Workat a distance if possibly .
Takenecessary precautions .






 
Therésistance of various types of materials are different . for instance . gold isa better conductor of electricity than copper .

Sorry for nitpicking, but isn't copper is a better conductor than gold. Gold is better for using in contacts, as it is more resistant to oxidization. Silver has less resistance than copper.
Thanks for the posts, these are great for revision, and I couldn't resist but to comment, as I thought this myself before I lost the argument. lol
 
Last edited by a moderator:
Measuring InsulationRésistance . ( IR ) Motor Testing ( 2.99MΩ )

SubstationMain Board – Main Sub-Board

ControlPanel . - Local Isolator / in ON position “ Phases Disconnected “
Motor Terminals must be Disconnected .

EarthContinuity . Plus ( R1 + R2 ) – CPC Disconnected “ Cross – connected
Linkingeach line conductor to Earth . This will check Polarity as well .

The Polarity of a Three-phase motor is normalchecked by the correction rotation .( 0.11Ω )




 
EarthFault Loop Impedance . will also need to be measured with the terminals’ disconnected .

To do this Live canbe a little bit awkward . To avoid the complication .The measurements of ( R1 + R2 ) are simply added to the Earth Loop Impedance ofthe Panel & NOTmeasured Live .

Zs = Z panel + ( R1 + R2 )
 
UsefulJunk .

Megger.

IlluminatedSwitched Probe - SPL 1000 . MFT1502 /1553 only . :43:

TheIlluminated Switched Probe accessory replacesthe RED 4mmtest lead .
Itcan be used anywhere that the 4mm lead set is specified in this user guide . &it will add Extra Résistance to a Loop Test measurement . ◄◄

 
( EFLI :- Earth Fault LoopImpedance )

BS-7671:2008– Red Cover . 17[SUP]th[/SUP] Awareness

Part7 – Special Installations or Locations .
753– Floor & Ceiling heating systems .

Ifwe look at the Regulations . “ General Requirements

753.1. Scope .
Thissection applies to the installation of electricFloor & Ceiling heating systems .
Eitherthermal storage or direct heating systems .

Itdoes NOT apply to wall heating or Outdoorheating systems .

YourConcern . The risk is One of penetration of the Element. :35:

 
EarthFault Loop Impedance . :49:

TheImpedance of the Earth Fault Current Loop starting & ending at the point ofEarth Fault .
ThisImpedance is denoted by ( Zs )
TheEarth Fault Loop comprises the following . starting atthe point of Fault .

- Thecircuit protective conductor .
- Theconsumer’s earthing terminal & earthing conductor
- For. TN Systems . the metallic return path .
- For. TT & IT Systems . the earth return path .
-The path through the earthed neutral point of the transformer .
- Thetransformer winding .
- TheLine conductor from the transformer to the pointof fault .
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K
I've just spent an hour getting bogged down with the maths trying to work out diversity for 2 cooking appliances on the same circuit (32A MCB)...
Replies
36
Views
16K
Greetings everyone. My first post here, having read a similar thread, I understand that following the manufacturers guidance is all important...
Replies
10
Views
8K
Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock