Hi Guys,

Apologies if this is a basic question for most of you, but i haven't had much if any experience with contactors. Basically we have been asked to quote to fit a timer to an industrial oven (63A) so it will switch on at 4am and warm up before the bakery opens so they can get on with baking straight away....Strange i know, but the customer is adamant that its done this way. My thoughts were a simple timeclock, and then a contactor to switch the oven? Am i right or totally wrong? Anybody done anything like this before? Or even have a drawing?

Thanks in advance
 
If it's a 63 Amp oven you'll need a substantial contactor and an enclosure to house it.

Can't you add the timer to the oven itself and maybe replace the on/off control switch with an ON/OFF/ON cam switch and re-designate it Auto/Manual? This wouldn't require any extra switchgear if it can be done.
 
If it's a 63 Amp oven you'll need a substantial contactor and an enclosure to house it.

Can't you add the timer to the oven itself and maybe replace the on/off control switch with an ON/OFF/ON cam switch and re-designate it Auto/Manual? This wouldn't require any extra switchgear if it can be done.

I'm not sure about this option although it would be by far the easiest, I had a look at the oven and the only way they seemed able to turn it on was via the rotary isolator on the wall. The only dials on the oven were from temperature adjustment. It's a massive 5 Door 6' x 6' x 6' industrial oven. Never seen an oven as big in my life.
 
I'm not sure about this option although it would be by far the easiest, I had a look at the oven and the only way they seemed able to turn it on was via the rotary isolator on the wall. The only dials on the oven were from temperature adjustment. It's a massive 5 Door 6' x 6' x 6' industrial oven. Never seen an oven as big in my life.

Yeah, I did say 'if it can be done'. It's possible the thermostatic controllers are also used as the 'off' switch, they may even have separate contacts for the on/off function, you'd need to investigate. There's also the problem of where and how to mount the timer, it all very much depends on the layout of the oven. If it can be done it's a cheap and easy method but it's difficult to say without a make and model number or a few photos of the existing setup.
 
What I mean is, if the oven is properly installed to ensure that it's safe in normal use, what additional precautions are required to make it safe for use with a timer?

Nothing wrong with adding a timer at all, It's the operation of the oven in a premises that is totally unattended, that's the problem...
 
I wouldn't have a problem adding a timer as long as it doesn't breach your local regs. The oven will have safety devices built into it but it would be wise to check the regs first.
 
The oven that you refer to is called a deck oven. Been around them most my working life.

To be fair in most cases they are on for 16hrs a day and are left un attended for most of it.
 

Reply to Contactor to switch an oven in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
863
Hi All Struggling to install a bog standard light switch due to getting confused by different coloured cables. I'm an avid DIY but never had...
Replies
5
Views
1K
I was looking for some advice on common wiring styles for stairwell delay lighting circuits. So I can figure out what has been done in the...
Replies
9
Views
2K
Hi, Apologies if this is in the wrong forum. I do have another account on here which I would imagine is not allowed by admins - this account will...
Replies
31
Views
4K
Hello, Firstly, I'm aware other people have posted similar topics on this forum, I'm not trying to create a duplicate, but more looking for...
Replies
29
Views
12K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock