Not quite understanding your question. Is this a new circuit? Are you after a contactor for a DOL starter or something?
 
As above ^^ are you asking what size for a DOL motor wired in a delta config' or for one of the 3 contactors that is in a Star/Delta arrangement.
Shall we assume the motor is a standard squirrel cage induction motor!
 
Not quite understanding your question. Is this a new circuit? Are you after a contactor for a DOL starter or something?
This is an existing circuit with 3 contactors to start and run the motor (soft start). The delta contactor has burnt out (AC3 10 Amp) therefore my calculations for a 15 Kw motor suggest the contactor is operating at its maximum and as it has burnt out before (im being told) I will suggest a higher rated AC3 contactor. The question was initially submitted to just see if any other person had come across these conditions. Cheers
 
So now it’s a Y∆ starter not DOL. How about giving us a clue as to what’s on the rating plate.

PS look up Y∆ starter, pay attention to the sizing of contactors.
 
Have you details of existing star,delta and main contactors? Are you sure failure was due to wrong contactor? If supplied with control gear,it was probably selected to suit...Have other aspects of machine been tested? As per Yoda, information wanting more of we are...
 
The guy clearly doesn’t know what he’s doing.

My holistic helmet is away for recalibration so I’ll leave it to the rest of you to carry on.

AmazingKarnak.jpg
 
In the OPs defence Tony, I'm the first one to mention DOL starter.

OP: Give us more info and we should be able to help. 10A looks low.
Who designed this starter?
What does the info on the motor plate say?
What type of motor is it and what is it operating?
Pics would be great of existing set-up and motor plate.

Could always google Star-Delta starters and check out what contacts they use for a 15kW motor.
 

Reply to contactor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
1K
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
518
Hi is there any relays or contactors that will pull in with 0v. Just continuity. Need a pump to come on but the trigger gives no volts just...
Replies
11
Views
760
When working in a control panel. If I needed to replace a 3 phase contactor do I need to carry out a 10point check to prove dead on just the mains...
Replies
16
Views
1K
Evening all, I'm relatively new to the trade and have just moved house. Looking to rewire and was looking at a few things, could someone tell me...
Replies
10
Views
465

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock