Discuss Control panel feeder cable sizing in the Industrial Electricians' Talk area at ElectriciansForums.net

Lc1

-
Reaction score
22
Hi,
We have a control panel that has a vsd, plc and motor anti condensation heater. For a preliminary cable calculation for the control panel feeder cable and its associated protection, would we just total up the individual loads to arrive at an approximation and use this to size the feeder cable ?

Thanks
 
Hi,
We have a control panel that has a vsd, plc and motor anti condensation heater. For a preliminary cable calculation for the control panel feeder cable and its associated protection, would we just total up the individual loads to arrive at an approximation and use this to size the feeder cable ?

Thanks

Doing what you said above you would most prob get a cable that is oversized. All depends on the panel.... Not that oversized cables would be bad.

Give is the equipment figures and then tell us what you get.
 
If you are unfamiliar with the load requirements of the machine then discuss with the manufacturer, alternatively refer to the plate and/or information supplied with the machine as this usually specifies what KW rating or ampage it is and then size accordingly.
The only time you need to consider other factors is like high inertia loads where start up currents may remain higher for longer and thus impact on supply cable sizing.
 
Hi,
We have 43.5A for the drive and at this stage I have assumed 10% for the remainder.
So fuse size chosen is 50A and 10mm2 cable based on the installation details.
 
You need to check the requirements of the drive, the drive manual usually expresses a minimum fusing to ensure you don't get nuisance tripping, if the drives pulls 44amps then it may recommend a 50 or 63rated.
Experience is good to have here because of the many variables, I'm guessing the drive is either 1ph - 3ph 11kw or 3ph-3ph 22kw given the values you gave.

I would on the limited info provided fit 63amp fusing and design the cable for 50amps load assuming your 10% covers all the other loads and max demand of the machine. Note dependent on installation conditions you may need to add additional earthing if you undersize the cable rating to the mcb/fuse rating.
 
Hi,
We have 43.5A for the drive and at this stage I have assumed 10% for the remainder.
So fuse size chosen is 50A and 10mm2 cable based on the installation details.

What sort of ambient? I take it this is in a conduit?

By instinct since it's fused down anyway, I would go for 16mm2. Unless perhaps it was always likely to be relatively cool in the space and the box I was feeding into was particularly tight/awkward.
 
Hi,
We have a control panel that has a vsd, plc and motor anti condensation heater. For a preliminary cable calculation for the control panel feeder cable and its associated protection, would we just total up the individual loads to arrive at an approximation and use this to size the feeder cable ?

Thanks
Voltage? Distance from POS? Number of Phases?
 
@Lc1

Your profile is still down as Trainee, are you still training or been some years ago are you now on the tools independent or with a company?
 
Hi,
Voltage is 400v 3 phase 50hz Distance is approximately 30m.

Thanks

With the known current requirement being around 50a, you're potentially approaching the limit of 10mm2, especially if there is the potential for it get warm. Seems like it's easiest to just fit a 63a isolator socket. Run a 16mm2 H07 from that. You can get the sockets with module space if you wanted to step down to 50a MCB and/or also RCD.

Leaves capacity for future expansions or replacement, and it's a fairly standard industrial solution. I'm pretty sure no-one would question it.
 
I have to congratulate the guys here, how they managed to give the OP an answer from the info in the OP is beyond me. The guys on here are very helpful, fair play.
 
I have to congratulate the guys here, how they managed to give the OP an answer from the info in the OP is beyond me. The guys on here are very helpful, fair play.

Not sure the answer exists just yet. 30m and we don't even know the ambient temperature or how the cable is to be run.

Although I'd be surprised if the final conclusion was anything less than 16mm2. 10mm seems a bit stingy, especially given the length.
 

Reply to Control panel feeder cable sizing in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
858
Hi, thanks for reading this. Ive been asked to look at a job where the DNO connection (single phase 80A TT) is a long run to the final circuits...
Replies
4
Views
277
Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
548
I’m running wires to the basement for future basement finishing. I’d like to add two circuits of outlets (one on the finished side and one on the...
Replies
0
Views
596
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock