hi guys

just been asked to have a look at a cooker tripping an rcd, its a split board single rcd.

she changed the element and didnt have any problems for a month. now all of a sudden the cooker is tripping the rcd after 10minutes of it been on.

any suggestions on what could be causing this, before she buys a new cooker?

cheers
 
Could still be the element (even tho fairly new), elements take a while to get to full working heat capacity and therefore can wait a little before thy trip, try an IR test on the element
 
sounds like another element has gone. you can IR it cold and it may show clear. with the back off the cooker, switch each element on one at a time till you find the one taheat's causing the problem. then with that element dissed, IR the bugger hot at 1000V.
 
Yeah, could be a pattern part ( cheap foreign copy) rather than original part, or just happened to be faulty outta the box, it does happen sometimes
 

Reply to cooker tripping rcd in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock