Discuss Cornrr taped and center taped deltas. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

D

dfloodhvac

Sooo I'm an hvac technician with a through understanding of electricity. And today i ran across a Y to delta step up transformer installation with a corner taped grounded delta secondary side... this was a Y 208va primary delta step up 240 va secondary.... funny thing was whoever installed this step up corner grounded delta tried to bond a neutral with the corner taped ground in an attempt to pull 120 va circuits. Now i know a corner taped delta can't be neutraled for 120 power because the corner ground is at phase voltage. But can i pull a neautral bus from the supply 208 Y transformer in order to pull 120 power. And is this code??
 
There’s several things of concern:


  • Very few UK electricians, unlike me, understand corner and centre grounded ∆.
  • I'm an hvac technician with a through understanding of electricity” so as you’re not an electrician to would be remiss to advise you.
  • Very few UK electricians, again unlike me, have a copy of the NEC code.

I’ll give you a hint, look at section 250 in the NEC code book.
 
Last edited by a moderator:
Alright god.... it just erks me wen electricians think they're holier than thou. Unfortunately you dnt kno wat ur talking about. I dnt need theory.
 
Sooo I'm an hvac technician with a through understanding of electricity. And today i ran across a Y to delta step up transformer installation with a corner taped grounded delta secondary side... this was a Y 208va primary delta step up 240 va secondary.... funny thing was whoever installed this step up corner grounded delta tried to bond a neutral with the corner taped ground in an attempt to pull 120 va circuits. Now i know a corner taped delta can't be neutraled for 120 power because the corner ground is at phase voltage. But can i pull a neautral bus from the supply 208 Y transformer in order to pull 120 power. And is this code??

So why are you asking the question

Alright god.... it just erks me wen electricians think they're holier than thou. Unfortunately you dnt kno wat ur talking about. I dnt need theory.

it just erks me wen hvac technicians think they're holier than thou.

No actually it really pi$$e$ me off when dicks like you take an attitude because the answer you want isn't forthcoming. Would you care to tell me the best way to regas my aircon probably not but hey wow poo happens
 
The funny thing is real hvac techs can easily transition to electrical work...... i know what problem and its alrdy been fixed to code i electricians are dumber than a box of rocks light bulb changers.... get a life better yet get a technical trade tht actually requires analytical skill...
 
Yet another one who throws his toys out of the pram because he didn't get the answer he wanted.
Tell me, since it's acceptable for us to advise an hvac person where does the line get drawn for it to be acceptable not to advise someone?
Joiner?
Plumber?
Police officer?
Art teacher?
Nurse?
Just so as I know for later, since I'm as dumb as a box of rocks.
Idiot.
 
Sooo I'm an hvac technician with a through understanding of electricity. And today i ran across a Y to delta step up transformer installation with a corner taped grounded delta secondary side... this was a Y 208va primary delta step up 240 va secondary.... funny thing was whoever installed this step up corner grounded delta tried to bond a neutral with the corner taped ground in an attempt to pull 120 va circuits. Now i know a corner taped delta can't be neutraled for 120 power because the corner ground is at phase voltage. But can i pull a neautral bus from the supply 208 Y transformer in order to pull 120 power. And is this code??
Corner grounded delta is relatively common in USA. The centre (center) tapped winding is is sometimes called a high leg or a wild leg.

It sounds like you have an American design and that will be rated for 60Hz. If you intend to use it here, UK, that might be a problem. Things like motors and transformers may well saturate owing to the higher V/f ratio - 240/50 instead of 240/60.
There is no simple way round that.

If you want help with NEC code you might try here:

http://forums.mikeholt.com/index.php

in the NEC section.
There are people there who will be very helpful.

Like many forums, your first several posts will be monitored before they get posted.
And, FYI, profanities of any sort are not permitted.

To the admin here - I am a member there but I am not trying to poach membership.....
 
Thr line gets drawn as far as ur knowledge is capable of reaching which seems to a a general basic knowledge of nothing pertient nor applicably. Why don't u electricians all get together and discuss the line of professionalism you seem to lack... there's a reason why the industry is full of innept bulb changers...
 
Thr line gets drawn as far as ur knowledge is capable of reaching which seems to a a general basic knowledge of nothing pertient nor applicably. Why don't u electricians all get together and discuss the line of professionalism you seem to lack... there's a reason why the industry is full of innept bulb changers...

Your right it does report sent to mods

Typical HVAC tech full of hot air and $$$$
 
Yet another one who throws his toys out of the pram because he didn't get the answer he wanted.
Tell me, since it's acceptable for us to advise an hvac person where does the line get drawn for it to be acceptable not to advise someone?
Joiner?
Plumber?
Police officer?
Art teacher?
Nurse?
Just so as I know for later, since I'm as dumb as a box of rocks.
Idiot.
A tad harsh I thought.
 
As besoeker says this configuration is widely used in the US but scarcely at all in the UK, so posting about it on a UK-based forum is probably not going to get you a lot of good answers. The theory is the same the world over but the practice, for historical reasons, is quite different. In other words, the fact that Tony knows about this kind of hookup at all is testament to his wide-ranging knowledge and experience. I would hesitate to call him a bulb-changer although I suspect he could make quite a good job of that too :)
 
Corner grounded delta is relatively common in USA. The centre (center) tapped winding is is sometimes called a high leg or a wild leg.

It sounds like you have an American design and that will be rated for 60Hz. If you intend to use it here, UK, that might be a problem. Things like motors and transformers may well saturate owing to the higher V/f ratio - 240/50 instead of 240/60.
There is no simple way round that.

If you want help with NEC code you might try here:

Mike Holt's Forum

in the NEC section.
There are people there who will be very helpful.

Like many forums, your first several posts will be monitored before they get posted.
And, FYI, profanities of any sort are not permitted.

To the admin here - I am a member there but I am not trying to poach membership.....

So am I, I'll give him a warm welcome there as well. Not that I think he would last long.
I'm also on CR4.
 
Incompetence.....

Just remember we don't use any of these systems over here! We don't have centre-tapped delta, wild legs or any such thing, so an electrician isn't incompetent not to know about them, just unfamiliar with overseas practice. Are you familiar with the crossed-ends test procedure for a ring-final?
 
Thr line gets drawn as far as ur knowledge is capable of reaching which seems to a a general basic knowledge of nothing pertient nor applicably. Why don't u electricians all get together and discuss the line of professionalism you seem to lack... there's a reason why the industry is full of innept bulb changers...

Your attitude stinks ...you are correct the industry is full of inept bulb changers it has been for yrs but Tony the guy you attacked is not one of them and is a very knowledgeable guy who has a lot to offer the forum and he'd be the first one on here I'd recommend having a chat to if you have Tx or Motor issues as he's spanned most his life in that field....

He directed you the section to look up in the NEC code, these are not cheap to purchase so why should he reel off the regulations for free.... I suggest you pick the toys up you threw out of the pram and try starting again .... coming on the forum and slagging off members will see you banned you came for help here so don't throw it back in our faces when you are given it, just because it means you will have to do some searching yourself and its not as direct answer as you wanted is no reason to attack members of the forum ....

Hope you get this post before your banned ...rant over:veryangry2:
 
In other words, the fact that Tony knows about this kind of hookup at all is testament to his wide-ranging knowledge and experience. I would hesitate to call him a bulb-changer although I suspect he could make quite a good job of that too :)
I don't think the OP called him a bulb changer.
 
Btw electrician... corner grounded deltas don't have a wild leg.... tht would be a center taped delta..... to whoever posted earlier
It was me.
You are quite correct.
You didn't mention a centre tapped winding.
But some installations do.

Anyway, take heed of my point about the different frequencies.
 
The joys of the wonderful American distribution system.

For “wonderful” read total lash up, it has to be one of the most dangerous systems in the world.

I’ve only ever got my hands on a centre grounded 480V system once. Can’t say I was too impressed with it and was trying to get it to comply with UK standards.
I gave up with that idea and phoned a company I used to work for and borrowed a 150KVA 433/500V Yyn transformer for a week. Fortunately they were one of our suppliers and happily lent it to us.

It was an odd beast I’d had made about 25 years before when changing over supplies to a plant. The secondary could be either voltage, the tappings gave it a 10% voltage adjustment.
 
He called all electricians bulb changers

I think he is a bored HVAC tech that is recovering at home because of the injuries sustained on site

if he's a HVAC tech, then he should be able to chill out.:6:
 
It could be taped without being tapped. Or maybe the tapping is taped. Take a tip: you can't top a well taped tapping.

Sorry I'm bored with my invoicing...
 
The funny thing is real hvac techs can easily transition to electrical work...... i know what problem and its alrdy been fixed to code i electricians are dumber than a box of rocks light bulb changers.... get a life better yet get a technical trade tht actually requires analytical skill...
Okay, on that note thread closed.
 

Reply to Cornrr taped and center taped deltas. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

This must be such a noob question but I cant seem to find any answer out there: Background: Installing a 10hp Air Compressor 230V 30A 3Ø. The...
Replies
8
Views
1K
Hello everyone. I'm in training but we haven't seen transformers or how they work yet. I have a transformer here I'm trying to figure out. There...
Replies
7
Views
1K
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
We've been tasked to run power to some electric motors on some pumps and the building is currently 120/208vac 3ph. The motors are 230/460vac 3ph...
Replies
4
Views
1K
220 vs 240 outlet questions I have a question understanding the difference between 220 volt outlets and 240 volt outlets. I saw a video online of...
Replies
16
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock