The car battery test is a good one, but make sure you include an appropriate fuse. If there is a fault, the much higher current available from the battery could fry the motor and invalidate the warranty even if the pump was faulty from new, as the makers stipulate a 5A fuse.

Alternatively, just measure the voltage at the pump leads with a DC voltmeter - 12V +/- 1V would suggest a pump / pipework problem, anything less suggests the supply is inadequate. This is quite possible - the normal running current is shown as 3.5A but this is an average figure. A single-diaphragm pump such as this has a pulsating load that peaks once per stroke, that might peak over 5A especially when starting (although not long enough to affect a 5A fuse). Starting from rest could be tripping the supply into 'foldback' immediately, where the voltage drops away to reduce the current to a low value, until the load is removed to trigger it to reset.

I would not have chosen a power supply intended for LEDs, I would be looking more at a 10A / 120W general purpose supply. Note that an electronic power supply behaves quite differently from a traditional wirewound transformer-rectifier when faced with an awkward load. A transformer will ride it, and just droop a little, eventually overheating if heavy overload continues for too long. An electronic one is more likely to go into some kind of protective mode even on a very brief overload such as starting a motor.

If memory serves right, these pumps make about 120 strokes per minute (don't quote me on that). From the rate and the sound one can usually tell whether a diaphragm pump is stiff, or the pipework obstructed, or the supply is faulty. Or maybe I've spent too much of my life lying in bilge listening to pumps and generators and things.
 
Thanks Lucien Nunes for the comprehensive reply. I have now carried out the car battery test, with the 5A fuse in line and achieved a wonderful 14-15 L/min. Completely different from before so I am pleased with that. All I need now is the correct transformer. I note your comments on transformer but I am a complete novice with this sort of thing. Can you give me a few hints as to what I should be looking for. I will probably buy from Ebay. I did wonder about the LED transformer but it didn't cost much.
 
Don't know how to put links on here but Google "Roy Pow C120 power supplies" which sell on Amazon, they do a power supply which is recommended for appliances powered by car 12v power outlets. They suggest it can power compressors and the like.
 
Last edited:
Don't know how to put links on here but Google "Roy Pow C120 power supplies" which sell on Amazon, they do a power supply which is recommended for appliances powered by car 12v power outlets. They suggest it can power compressors and the like.
Thanks, I will have a look at it.
 

Reply to Correct transformer for 12V waste water Pump. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Is there such a thing as a double breaker that has a separate DC and AC line passing through it? I need a 12v (25 amp) line and a 240v (15 amp)...
Replies
1
Views
686
Hi, I understand some basics about wattage, volts and amps etc but I am trying to decide what would be the most efficient system Situation - 2 x...
Replies
18
Views
2K
Hello, I am fitting a Telecom 8 Compact burglar alarm system to a boat. The boat has both nominal 12v DC supply (ie up to 14.2 v when engine...
Replies
2
Views
723
Hi, Been looking to replace a set of downlights that have seen better days. Been doing some checking of what's in place to see whether it's just...
Replies
3
Views
964
Hi, I hope that someone here might be able to put my mind at rest. I have an engineering mind and a reasonable understanding of electical work...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock