So I will use something like this (found a type A time delay) which I will put in a separate enclosure to replace that 100A isolator.


If those fusebox rcbos aren't switched neutral your gonna have a problem....

The tails appear to all be visible there so I wouldn't add upfront rcd protection to anything other than the submain going off to the kitchen.
 
If those fusebox rcbos aren't switched neutral your gonna have a problem....

The tails appear to all be visible there so I wouldn't add upfront rcd protection to anything other than the submain going off to the kitchen.
They are definitely DP as they're the mini ones.

I'm a little confused as to why you say a upfront for the whole system isn't required? I was led to believe when I did my course (granted I think 'guru graham' as I used to call him was good at passing off his thoughts as a regulation sometimes) that on a TT it must have upfront RCD to protect the tails regardless.

I need to make sure this one has no hiccups as it will be looked at by my CPS assessor so that I can pay for the privilege of being a member for another year....

So I am not questioning your judgement. I just need to know how that fits into the regs as my understanding is its a no ifs, buts or maybes. But could be the way I've had it explained.
 
Just did so quick research and can find nothing to suggest Fusebox have made full height RCBOs that switch both poles. Their new AFDD RCBOs are tall and switch both poles.

Yeah I think I have gotten it confused with the mini ones and the AFDD ones I was quoting for the other day (some bloke wanted all 14 circuits protected with AFDD! Soon changed his mind when I told him that was £1750 before we even started on the remaining materials and labour etc)
 

Reply to Correct Type-S Upfront RCD for 3Ph TT System in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi, I was wondering if the wylex/Proteus SPD Isolators where dual isolator, they have 4 terminals at the bottom, can you use them to take 2 sets...
Replies
20
Views
3K
Hi all, First time post to the forums, I hope you all go easy on me! We are undertaking an electrical install as apart of a solar PV...
Replies
5
Views
982
I am going to need to install a small amount of galvanised steel conduit, leading down to perhaps 4 sockets and a light switch. This is in a...
Replies
38
Views
4K
I don't think I have worked with 32mm conduit before. Always 25mm and 20mm. I want to contain 2 x 25mm tails and 1 x 16mm earth in some 32mm...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock