If the interconnection cable is elv band 1 and a 3core is installed between heads using a core as the interlink isnt this aggainst reg 528.1 (segregation of band 1& band 2 cables)
 
No it's covered by 528.1 (ii)
Quoted from the thread I linked at the start:

Either way if it is 230v AC or a 9v DC signal..
The conductor it travels down should be insulated along its length as either

a) if at 230v it is a live part and must be insulated or out of reach etc... 416.x.x

b) if at 9v (or similar) it is mixed voltages in the same cable and conductors should be insulated to the level of the highest voltage present! 528.1 (ii)
 

Reply to CPC used as interconnect on smoke detectors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Prompted by the other thread.... I had a slight dilemma on this topic a couple of days ago. Three mains smoke alarm bases, on their own circuit...
Replies
9
Views
2K
Just wanted to get peoples opinion regarding a job ive been asked to do. The customer wants improved fire detection in there property, which is a...
Replies
19
Views
2K
D
I carried out the new PIR / condition report today and found a diy bodger had added two way light switching, in flex ,using the cpc as a live, in...
Replies
25
Views
14K
Graeme Harrold
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock