Discuss Crossover in ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Sorry I thought you wanted to remove a dumb rating that you had made.
 
About time ring circuits are banned....just a nuisance IMO in terms of testing, finding faults.
I remember reading somewhere that the ring main(as it was called then) came about after the 2nd world war when copper was in short supply, so the ring circuit was utilised, as prior to that they used radials.....and aren't we the only country to use them?
 
About time ring circuits are banned....just a nuisance IMO in terms of testing, finding faults.
I remember reading somewhere that the ring main(as it was called then) came about after the 2nd world war when copper was in short supply, so the ring circuit was utilised, as prior to that they used radials.....and aren't we the only country to use them?
I couldn't disagree with you more. Ring finals are a very versatile circuit, when used in the right situation. Sure, I install more radials than I used to, but a 32A ring is often preferable to say a 32A 4mm radial, which you'd struggle to install in a compliant manner unless clipped direct through it's whole run. And we aren't the only country to use them! But even if we were, surely that's another reason to keep them. A Great British innovation.
 
I couldn't disagree with you more. Ring finals are a very versatile circuit, when used in the right situation. Sure, I install more radials than I used to, but a 32A ring is often preferable to say a 32A 4mm radial, which you'd struggle to install in a compliant manner unless clipped direct through it's whole run. And we aren't the only country to use them! But even if we were, surely that's another reason to keep them. A Great British innovation.
I was maybe a bit harsh in having them banned!
Yes there are situations where a ring circuit is better e.g. sockets in a long corridor or a large hall. I do a lot of EICRs in university buildings and sometimes there's dozens if not hundreds of RFCs that have maybe five or six sockets on them, usually 4mm and in dado trunking with the DB in the same room or close by, and I just think, surely they could have put in a 4mm radial. I guess I see them as more work compared to radials!
 
Yes there are situations where a ring circuit is better e.g. sockets in a long corridor or a large hall. I do a lot of EICRs in university buildings and sometimes there's dozens if not hundreds of RFCs that have maybe five or six sockets on them, usually 4mm and in dado trunking with the DB in the same room or close by, and I just think, surely they could have put in a 4mm radial. I guess I see them as more work compared to radials!
nah, pull your 2 x T+E 2.5 cable to the last socket, then pull loops out at wherever you need them along the run, not much more effort than a radial
 
nah, pull your 2 x T+E 2.5 cable to the last socket, then pull loops out at wherever you need them along the run, not much more effort than a radial
Yeah it isn't much more work when installing, but when there's a 36way 3phase board with about 20 odd RFCs in it to test on an EICR, then after a while you get fed up of disconnecting the legs and fannying on with tyrapped cables:mad:
 
Yeah it isn't much more work when installing, but when there's a 36way 3phase board with about 20 odd RFCs in it to test on an EICR, then after a while you get fed up of disconnecting the legs and fannying on with tyrapped cables:mad:
yea, especially when some dougnut has twisted the earths together all the way back then popped their sheath on, makes a 2 minute job take 5

ive never done student accom though so cant say ive ever come across that many rings on 1 board :D
 
yea, especially when some dougnut has twisted the earths together all the way back then popped their sheath on, makes a 2 minute job take 5

ive never done student accom though so cant say ive ever come across that many rings on 1 board :D
Ah yes two earths twisted in one sleeving.....thats the sign of an electrician who doesn't worry about the testing!
I do accommodation and academic buildings, the biggest EICR I did was the Engineering department, over 400 pages! And took about 8 weeks in total! It's a joy when they say you can't turn the sockets off.....great less for me to do and LIM in the boxes:)
The Chemistry department is even bigger, due next year...dreading it:eek:
 
The RFC is unique to the UK, IMO very clever system, and I hate it when guys moan about it, when testing faulting etc , you are all just lazy.
Yes I am lazy!:p Anyway there's a night shift coming up soon to do an EICR in a large Uni office building......no RFCs.....it all radial circuits busbar trunking and floor sockets! Woohoo!:cool:
 
Yes I am lazy!:p Anyway there's a night shift coming up soon to do an EICR in a large Uni office building......no RFCs.....it all radial circuits busbar trunking and floor sockets! Woohoo!:cool:
i thought i had it bad other day with a 25 circuit test split between 5 boards, any industrial/commercial i have done its been radials for the most part, and maybe a ring for the office area, rest is 3 phase machinery which is a doddle to test.

the effort they put into twisting the earths all the way back with pliers is probably more than it would take to individually sleeve them, at least i know when i leave a job nobody is going to be cursing my name when it comes time to replace anything lol
 
Ah yes two earths twisted in one sleeving.....thats the sign of an electrician who doesn't worry about the testing!

I know it infuriates me too! .

I pull a guy up on it once and he told me "it was because he didn't want to wast the Earth sleeving"....!!!!.???.!!! :mad:
It's £5 for a hundred meters!!!!!!
It's a shame he didn't have that concern with the Bloody Cable!!!!!......... I Wounder Why that is..
 
I know it infuriates me too! .

I pull a guy up on it once and he told me "it was because he didn't want to wast the Earth sleeving"....!!!!.???.!!! :mad:
It's £5 for a hundred meters!!!!!!
It's a shame he didn't have that concern with the Bloody Cable!!!!!......... I Wounder Why that is..
sounds like if you asked some of these sparks to build you a square room you would end up with a sphere shaped room, cut all the corners ;)
 
it’s good practice [...] keeping the first 2 legs from the consumer unit short as possible
Actually not, in terms of imbalance, the reverse is true (although you still need to watch the Ze at the furthest point)
To illustrate I'll start with spinlondon's excellent example:
Ok.
If you have a ring that is 4m long with 3 sockets each 1m apart, the middle socket would have the same resistance on each leg. The other two sockets would have different resistance on each leg at a ratio of 3:1.
A 20A load connected to the middle socket would see 10A on each leg.
A 20A load connected to either of the other two sockets would see 15A on the short leg and 5A on the long.
Suppose we are worried about imbalance, so we shorten the two legs to the CU to 0.5m each.
The other two sockets would have different resistance on each leg at a ratio of 5:1.
A 20A load connected to the middle socket would see 10A on each leg.
A 20A load connected to either of the other two sockets would see 16.6A on the short leg and 3.3A on the long!

If you follow my suggestion and we make a loop of slack and extend the two legs to the CU to 2m each.
The other two sockets would have different resistance on each leg at a ratio of 3:2 i.e. 1.5:1.
A 20A load connected to the middle socket would see 10A on each leg.
A 20A load connected to either of the other two sockets would see 12A on the short leg and 8A on the long. Much better.

Hope this helps.
 
Actually not, in terms of imbalance, the reverse is true (although you still need to watch the Ze at the furthest point)
To illustrate I'll start with spinlondon's excellent example:

Suppose we are worried about imbalance, so we shorten the two legs to the CU to 0.5m each.
The other two sockets would have different resistance on each leg at a ratio of 5:1.
A 20A load connected to the middle socket would see 10A on each leg.
A 20A load connected to either of the other two sockets would see 16.6A on the short leg and 3.3A on the long!

If you follow my suggestion and we make a loop of slack and extend the two legs to the CU to 2m each.
The other two sockets would have different resistance on each leg at a ratio of 3:2 i.e. 1.5:1.
A 20A load connected to the middle socket would see 10A on each leg.
A 20A load connected to either of the other two sockets would see 12A on the short leg and 8A on the long. Much better.

Hope this helps.
F#ck me you need to get out more !
 

Reply to Crossover in ring circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock