Hi chaps.
What are the permitted zones for concealed wiring feeding Dado trunking?
I am doing a small class room extension and the architect wants the pvc conduits that drop down from the suspended ceiling to feed the Dado concealed in the stud wall. Is this permitted?
Cheers

Lee
 
Zoning is the same as any other situation but caution here as the trunking is surface mount you shouldn't apply vertical zoning to the socket as its positioning isn't fixed a trunking corner drop or mid drop is best in the same trunking used for the DADO this allows data cables etc to be wired in too, if you wish to do as the Architect asks then IMHO it will require mech' protection if <50mm.
I always design the drop by the door which allows light switch to be fitted within the trunking.

I suspect others may disagree as this is my personal practice as i see a conflict where dado trunking is used and vertical zoning, the trunking allows for flexibility and repositioning which often happens so always best to avoid out of zone issues arising.
 
Hi chaps.
What are the permitted zones for concealed wiring feeding Dado trunking?
I am doing a small class room extension and the architect wants the pvc conduits that drop down from the suspended ceiling to feed the Dado concealed in the stud wall. Is this permitted?
Cheers

Lee

Of course it's permitted!!
Just take the precautions and suggestions that darkwood pointed out...
 
agreed. much better to put the drops in trunking. tell the archydick to stick to the drawing board and accept your expert advice on safe cable routeing.
 
Conduit drops in stud wall is ok make sure that you have enough drops for the amount of data and mains cables. Separate drops of course. I allow 6 utp cat 5e cables per 25mm conduit. The reason for the conduit drops is that the customer or architect only want horizontal dado runs not vertical as they think it is not esthetically pleasing and leaves maximum wall space.
 

Reply to Dado trunking feeds in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
866
I am going to need to install a small amount of galvanised steel conduit, leading down to perhaps 4 sockets and a light switch. This is in a...
Replies
38
Views
4K
I am connecting a manual transfer switch to a subpanel. In order to minimize drywall work, I am mounting the transfer switch to the surface of the...
Replies
3
Views
1K
Hi there - good site. Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline)...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock