Dartlec

Esteemed
Arms
Reaction score
2,441
Had a nightmare of a day trying to get a small 2 bed 1900 or so terrace house through its EICR today for the landlord.

He's one I work for, so its a case of fix as I go to get a satisfactory rather than just report.

2-3 hours was sorting out the downstairs lighting circuit failing on IR L-E with 0.44MOhms (all loads removed)

Not much left of the in wall back boxes but even with everything pulled out, the main problem turned out to be a short switch extension in 3 core and earth from one room to another. (perm live to switch, 2 switched lives back)

Nice pictures of what remains of the back boxes....

Switch 1 - Copy.jpg Switch 2 - Copy.jpg switch 3 - Copy.jpg

Only one of the cores was failing (perm live), so with some rejigging of switch locations I managed to get things to pass for now at 2.4MOhm on 500V (though bizarrely was getting 0.7 on 250V). Had to put surface pattresses for now though to get the switches back functioning.

It's fairly clear that the switch drop cables have been affected by the damp - the ends of all cores were that dull black, and cpc was bright green in places.

Some remedial work has been done for the damp, so this may be historic damage, but given the age of the house it might also be impossible to completely solve.

The wiring at light level seems fine, it's only the switch drops that have been affected from what I can see - unfortunately I think they are in junction boxes somewhere in the ceiling, not at the pendants so rewiring will likely be fiddly and disruptive - though it will likely have to be done at some point.

Questions:

Once a cable like this has been affected, does it usually get worse over time, or will it stabilise if no more damp occurs? I'll probably be recommending an annual test on this circuit for a while anyway - not currently RCD protected though I'll be recommending a board change.

Is there a proven way to protect cables from damp in a wall?

One thought is using Quinetic or similar to avoid switch drops on the walls in question. Any other ideas in similar situations? The sockets were (badly) rewired some years back for I suspect the same reason in surface mounted 25mm conduit, which as you can imagine looks lovely... so I'd rather avoid that as an option...
 
I would imagine that putting in plastic trunking / conduit for the cable and plastic back-boxes would provide good protection for anything buried in a damp wall's plaster or cement, so long as some means for air circulation / vent to the pipework?

RCD protection would be sensible, as clearly that circuit is a bit dodgy. No idea if it might fail in a fire-starting manner (probably not if the wall is not inflammable) but for T&E I suspect the RCD would trip on any serious insulation failure as it would be to earth first, not live-neutral.
 
Last edited:
There was a thread recently where some NI sparks were saying that they always put in plastic conduit for wiring in domestic installs, even if T&E is used. This would be a perfect use-case!
 
I would imagine that putting in plastic trunking for the cable and plastic back-boxes would provide good protection for anything buried in a damp wall's plaster or cement, so long as some means for air circulation / vent to the pipework?

RCD protection would be sensible, as clearly that circuit is a bit dodgy. No idea if it might fail in a fire-starting manner (probably not if the wall is not inflammable) but for T&E I suspect the RCD would trip on any serious insulation failure as it would be to earth first, not live-neutral.
The damp might put out any fire at least!

I wondered about burying plastic back boxes in the wall in this case, though I generally consider it a bodge when I see it. Conduit boxes with plastic conduit could work I guess though.

It is at least only 2 main switch drops involved, and then a sideways switch extension that was done at some point due to door moving I think.

It may be possible to end the plastic conduit up the ceiling/floor void for ventilation - the damp doesn't seem to have reached that height. But I'm never a big fan of chasing walls, even less so when the room is already decorated. At the moment I think the wallpaper may be holding the plaster on the wall!
 
Hi,are you sure it is e degradation of the insulation,and not a localised or single,localised bit of damage,providing a path for your IR readings. The difference in readings on 250/500v may possibly be due to that path being cleared by a higher voltage,at a small,localised part,whereas a general failure of insulation,over a run,,would give a more consistent reading,over consecutive tests.

If it is one core in particular,which is giving a low reading,it points to a more definitive reason,rather than a overall clue,of the complete cables failure,due to damp.

I know it's probably more poking around,than it deserves,but by separating and disconnecting the cores,checking continuity/resistance,to confirm equal standing,you can IR individual cores,with reference to both earth and each other,with various alternative combinations,and build up an idea of what may be occuring.
 
There was a thread recently where some NI sparks were saying that they always put in plastic conduit for wiring in domestic installs, even if T&E is used. This would be a perfect use-case!
Conduit is the norm here in South Africa as well, it's pretty rare to see cables buried direct and I've never seen capping used.
 
I had exactly the same problem with a ring final circuit. The IR was 0.3 Mohm. The offending cable (after tracking it down) was buried in a wall which was absolutely sodden and the back box (galv) like yours was rusted away (so much for galvanised!) My answer was to chase out the cable completely and replace the cables via a hole in the ceiling I cut, and put them surface. IR was then 459 Mohm. We had to core drill through the same wall it took about four hours going through the wet wall, end terrace outside wall. It was soaked through and through. Interestingly, the more we removed of the offending cable the better the IR readings go. We chased a bit (meter) then tested, then another meter and so on when we got to the ceiling it was as above reading. So it is graded and gets worse the more cable that is in the wet wall.
 
More or less implying T&E is or becomes porous over a period of time but Ive known T&E installed (rightly or wrongly) outside in all weathers where its insulation has been and remained sound.
One such example, did an EICR the other day where a T&E fed a pond and was run (wont class as installed) in an open gulley (so IN water at various points and times). The IR was good >100M. Red & Black so probably in excess of 15 years old!
 
More or less implying T&E is or becomes porous over a period of time but Ive known T&E installed (rightly or wrongly) outside in all weathers where its insulation has been and remained sound.
One such example, did an EICR the other day where a T&E fed a pond and was run (wont class as installed) in an open gulley (so IN water at various points and times). The IR was good >100M. Red & Black so probably in excess of 15 years old!

More likely over the years the water has wicked up into the cable by capillary action.
 
Agreed that can happen but unless the insulation becomes porous or is damaged I would still expect a good IR.

But the inner insulation, not the outer. Which would explain why T&E outside in water is OK.
 
I had exactly the same problem with a ring final circuit. The IR was 0.3 Mohm. The offending cable (after tracking it down) was buried in a wall which was absolutely sodden and the back box (galv) like yours was rusted away (so much for galvanised!) My answer was to chase out the cable completely and replace the cables via a hole in the ceiling I cut, and put them surface. IR was then 459 Mohm. We had to core drill through the same wall it took about four hours going through the wet wall, end terrace outside wall. It was soaked through and through. Interestingly, the more we removed of the offending cable the better the IR readings go. We chased a bit (meter) then tested, then another meter and so on when we got to the ceiling it was as above reading. So it is graded and gets worse the more cable that is in the wet wall.
Sounds similar - the cable worst affected in this case had been run horizontally through the wall, though even then only one core to earth was giving me the failed readings so was able to reuse the other two for now.

I'm fairly sure I'll have to replace from ceiling down in conduit - It will be the landlords call whether I put it surface mounted or in the wall I guess - though based on drilling chasing won't be difficult, just messy.
 
Agreed that can happen but unless the insulation becomes porous or is damaged I would still expect a good IR.
I've certainly seen plenty of outside T&E to lights that's been exposed to weather for years and not damaged, but I guess you cable was probably terminated properly at both ends? I imagine this damage may have crept directly up the copper from the terminals, which were green and nasty...
 
Hi,are you sure it is e degradation of the insulation,and not a localised or single,localised bit of damage,providing a path for your IR readings. The difference in readings on 250/500v may possibly be due to that path being cleared by a higher voltage,at a small,localised part,whereas a general failure of insulation,over a run,,would give a more consistent reading,over consecutive tests.

If it is one core in particular,which is giving a low reading,it points to a more definitive reason,rather than a overall clue,of the complete cables failure,due to damp.

I know it's probably more poking around,than it deserves,but by separating and disconnecting the cores,checking continuity/resistance,to confirm equal standing,you can IR individual cores,with reference to both earth and each other,with various alternative combinations,and build up an idea of what may be occuring.
It's quite possible, though nothing obvious and by the time I'd got things to an acceptable level I'd had enough of poking around...

Unfortunately it looks like I can't get at both ends of the cable easily as they aren't junctioned at the pendant (might be above the ceiling there if I'm lucky) so not easy to separate legs.

I'm hopeful that if I track down the switch drop at ceiling height and test there things will be fine, then I can rejoint and run in conduit/trunking...
 
I had exactly the same problem with a ring final circuit. The IR was 0.3 Mohm. The offending cable (after tracking it down) was buried in a wall which was absolutely sodden and the back box (galv) like yours was rusted away (so much for galvanised!) My answer was to chase out the cable completely and replace the cables via a hole in the ceiling I cut, and put them surface. IR was then 459 Mohm. We had to core drill through the same wall it took about four hours going through the wet wall, end terrace outside wall. It was soaked through and through. Interestingly, the more we removed of the offending cable the better the IR readings go. We chased a bit (meter) then tested, then another meter and so on when we got to the ceiling it was as above reading. So it is graded and gets worse the more cable that is in the wet wall.
Surely the first thing to do in that situation is report the sodden wall to however and rectify the fault that made the wall that wet, only then should we consider replacing any effected items?
 
Surely the first thing to do in that situation is report the sodden wall to however and rectify the fault that made the wall that wet, only then should we consider replacing any effected items?
At least he's put a solution in place (surface wiring) so that they have the electric back on until the damp issue is fixed.
 
Surely the first thing to do in that situation is report the sodden wall
No, the first thing to do is report to the client a failure of IR leading to an unsatisfactory report. Finally bring to the attention of the person ordering the work the reason found for the problem and possible solutions in order to rectify the situation with the clients knowledge and contractual agreement. I was subcontracting to a building firm who were apprised of the situation, who in turn took it up with the client who in turn agreed a course of action and costs associated with that action. As to getting involved with the client (LL) it would not have been within my remit to do so it is up to the builder to action the damp wall. Which as a matter of interest had been treated by rendering and coating with rainproof exterior coating. Obviously didn't work judging by the coring and water encountered while doing so. But no building work is not my bag just the installation. Anyway by the time the owner had remedied the wet wall hell would have frozen over and he would not be able to rent the property thus losing money and then having none to fix the wall so......to avoid mission creep, best get the electrics fixed first eh?
 

Reply to Damp damage to cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
515
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
387
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
594
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
614

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock