Discuss Dimmer Flicker in the Australia area at ElectriciansForums.net

M

M Slingsby

Advice Please..

Installed a 1 gang double dimmer powering, on one side, a triple 3x50w halogen ceiling fitting. On the other side it powers 2 separate 50w halogen switched wall mounted spots connected part way down the line at a simple junction box housed in the roof-space.

The two separate spots flicker when the lamps are dimmed no matter which one or even if both are used. The ceiling fitting is fine.

The dimmer is a standard 400w 240-250v rotary push on-off plastic type.

Is this a dimmer fault or a wiring fault?
 
Last edited by a moderator:
Are the spots ELV fitted with a 12v transformer or are they GU10's? If powered via a transformer, you may have damaged it, as it may not be a dimmable type - seen some of these flicker before when used with a dimmer
 
just todat fitted a double dimmer. one of two wall lights was duff and the other one flickered when dimmer was between 1/3 and 2/3 up. replaced the duff lamp and it worked fine. these were incandecsent 40w candle lamps. could be something to do with not having enough load on the dimmer. sounds daft, but it could be
 
i find that having 2 dimmer coils on more than 3 fitings degrades voltage across the circuit , as a rule of thumb i never install 2 dimmers on a 2 way or intermediate circuit
 
Because of how the control circuit works in a standard dimmer, it is quite sensitive to fluctuations in line voltage and other distortions to the waveform of the mains.
Those with better filtering perform better in terms of nuisance flicker as a result.

The lower the PSCC is at the origin of the installation, the more prominent the effect will be. (The supply impedance is higher)

You also need a minimum loading, usually this is 40W, but some are 60W (not the OP's problem with 5x50W)

But if the ceiling fitting is DEFINITELY fine, I'd go check your junction box in case one of the conductors hasn't been properly gripped.

Simon.
 

Reply to Dimmer Flicker in the Australia area at ElectriciansForums.net

Similar Threads

I have purchased spotlights as below, but they are flickering when I dimmed them down to around 15-20%. We have installed 8 x ALUSSO LED Recessed...
Replies
4
Views
1K
Hi, in my bedroom i had a 2 gang dimmer that powered 2 set of 3 spot lights and also had passthrough wires to other sockets. Im changing to just...
Replies
2
Views
250
I purchased a house that has a really cool 12v halogen setup where two wires are suspended across the ceiling in two different locations, and each...
Replies
9
Views
923
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hi. In the images. One is a 2 gang dimmer switch and the other a normal 2 gang switch arrangement. Dimmer 1 controls the main ceiling rose and...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock