alan-c

-
DIY
Reaction score
2
I have just completed a stand alone (not grid connected) solar PV powered mains supply in my garage as mentioned in the thread "solar earthing question".

The Epever 1000W continuous inverter seems to be cutting out at low loads: I plugged in all my tool chargers (1 x 36v, 2 x 18v, 1 x 10.8v) estimated total load about 200-250W max and the inverter cut out after a couple of minutes. I tried again and added a 60W bulb to the load and it cut even quicker. With just a bulb and two soldering irons total 210W it ran for some time and didn't cut out. Then I tried a bench grinder (max 350W) and the inverter cut then restarted over and over gradually spinning the grinder faster until it reached a point where it would spin up to full speed without cutting out - I didn't bother trying to grind anything.

The above suggests that the grinder has a start up load much higher than 1000W due to the inertia of the wheels, but I can't see why the chargers would cause the inverter to cut; I plugged them in one at a time, no sudden load. Any suggestions before I contact the supplier? Also I don't know if it is possible to easily measure peak/transient loads.
 
I'd guess that one possible cause is that the load is too low. I would suggest you try it with a 800-900W mainly resistive load (like a small fan heater with just one element switched on) to see if it is better behaved at higher loads. If that works, all you can really do is try a variety of loads to find what works and what doesn't.
 
GeorgeCook, yes, the supply is a solar charged 24v 110Ah battery and the minimum voltage noted was above that at which the inverter cuts out according to the manual. I have tried higher loads, 1000W heater and 6000W toaster and it cuts immediately. I have written to the supplier and will report back when situation is resolved - or not.
 

Reply to Disappointing 1000W inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello, My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an...
Replies
2
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
Hello there I have just installed a new Solis S6-GR1P3.6K-M-DC Inverter - this replaced a 10 year old+ Sungrow inverter that failed/out of...
Replies
5
Views
2K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
445

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock