I would also be doing everything I could to rcd protect the armoured.

I agree about protecting the submain, but you don't want an RCD at source (Why?) as it would/could trip the whole of the remote installation on an earth fault which is a good 30 M away !, no, RCD's local if required is far better IMO, besides if the RCD was at source would this not contravene the regs wrt circuit segregation ? (314.1).

Unless of course the Installation was TT, and then a time delayed 100mA may be required
 
Last edited:
why on earth would you want to RCD the SWA?
 
Can of worms lads?

Gazz I'm not wet behind the ears you know I know about the 100A and the 16mm , and why would I RCD a distribution circuit in Armour????
 
Wouldn't that mean the only protection the 16mm would have is the 100A service fuse? I wouldn't even consider that as an option! I would also be doing everything I could to rcd protect the armoured.

Gazzdid, please explain your RCD suggestion on the armoured cable....?
 
I would have thought the 100A service fuse protecting the 30M run was a big no-no. If someone puts a spade through the SWA, the supply for the whole house is lost until the DNO comes out? Daz.
PS I'm no expert, so feel free to pull this comment to bits :smiley2:
 
I would have thought the 100A service fuse protecting the 30M run was a big no-no. If someone puts a spade through the SWA, the supply for the whole house is lost until the DNO comes out? Daz.
PS I'm no expert, so feel free to pull this comment to bits :smiley2:

nothing wrong with your comment. a 60A sw fuse is the answer.
 
Hence why you protect the cable using an over-current device.
 
Yep fair enough. Just saw a couple of posts on page 1 that seemed to be saying you don't need the fuse - seemed strange. Daz
 
Yep fair enough. Just saw a couple of posts on page 1 that seemed to be saying you don't need the fuse - seemed strange. Daz

The question wasn't should we or should we not install it as obviously we should. We were debating on where it should go in relation to the service head.

Overcurrent protection doesn't necessarily have to be at the origin of a circuit, (433.2 refers) but when it comes to the DNO, they are a law unto themselves so in this instance it would be best IMO to place it at the origin.
 
Just trying to get this straight in my head so apologies!

If the overcurrent protection is at the end of the 30M run, the scenario of a spade through the SWA will not result in the fuse blowing, but will blow the service fuse.

I thought if the 60A switch-fuse was protecting the cable it should go at the origin?

Daz
 

Reply to Distribution circuit question in the Australia area at ElectriciansForums.net

Similar Threads

I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
4K
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
298
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock