Discuss Distribution circuit question in the Australia area at ElectriciansForums.net

We're talking two different types of protection here I.e overcurrent & short circuit.

Before we were mainly talking overcurrent protection which ad I said previously can be placed anywhere along the circuit, (433.2.2)

Reliance on the suppliers fuse for short circuit is debateable and IMO in this instance wouldn't be accepted by the DNO should they find out.

Sent from my BlackBerry 9800 using Tapatalk
 
Problem Solved

Got a 100mm x 190mm metal clad enclosure with 80A main switch and 63A MCB, its proteus(CEF) so not the best but it will do the job at origin, im going to have to move the mainswitch slightly in the meter cupboard to fit it in but at its the best i can do

cheers for the input, ive enjoyed reading it all!
 
View attachment 10506

And if he was he may have used the attachment as a guide

I never use that table, the one originally posted by Spin in the same ''STICKY THREAD'', is the one to use, and have done for a number of years now. In your link a 16mm SWA cable fails to meet compliance for a XLPE 3 core cable, whereas in the alternative table it DOES comply.... It would also comply in 2 core 16mm form as well!!


Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
16
17
18
2.5
5.7
17
19
20
4
9.0
19
21
23
6
13.6
22
23
36
10
22.6
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
(452)
 

Reply to Distribution circuit question in the Australia area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
4K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock