Hi all.
I'm currently training as an electrician so would like your views on this for clarity and if I need to get someone in?
I have just moved in to a new (very old) house and on inspection of the CCU I noticed the incoming service cable from the overhead was chard at the top of the dno head.
UK power have been out ( literally within hours?) whilst I was at work and replaced the cable and installed a new fuse and DNO cut out with a PME TN-C-S. The house is on TT earth currently and at the bottom of the new cut out is a short run of earth with a clamp. Would I be right in assuming I can get someone to connect this up to the MET within the CCU making the earth stake redundant? I have posted a picture of the new installation.
IMG_20200527_234727.jpg
 
Last edited by a moderator:
You need to confirm that the bonding requirements for a PME supply are met before connecting to it.
TT can, and often will, have smaller main bonding conductors than are required for PME.

Also a general inspection will be required to confirm a basic level of safety before anyone does any work to the installation.
 
Indeed, also a chenge to the earthing arrangement will completely change the Ze of the installation. Although it will improve the EFLI, Zs for each circuit, it needs checking and documenting.

PS Would like to see a bigger view of all of the cabling, I'm interested in where the pair of (only 10mm?) L&N tails go to.
 
Also a lot of heavy cables. The stuff on the top-left looks bigger than the tails from the cutout, wonder if it is 16 at cut out and 25 on the top-left, or 25 / 35 for some odd reason?
 
If this was fairly recent, there might be a letter coming in the post to say it’s complete and safe.

The DNO won’t touch anything to do with the house installation, as we don’t do anything to their head and fuses.

Get someone in, although at the moment there’s nothing unsafe with using the old TT
 
Hi guys. Thanks for replying.

Yes as Snowhead said, the small tails supply the control /meter for the economy 7.

I'll grab another picture.

Also, as per some of your views I was surprised that the DNO put on a 100 A. Im not sure the meter tails are 25mm, I would assume that the DNO would have some liability to check before uprating the fuse?? I'm not aware what the old one was but, as far as I am aware its got to be 20+ years old, it's an oldish 2 rate digital meter........and an old clock style switch for the econ 7 storage heating. ...... My next job is to get on to the supplier to get them to come and check out to the CCU.
[automerge]1590668808[/automerge]
Do check the main RCD trips on test OK though!
Oh yes it works!
 

Attachments

  • 15906686359028344413392097815617.jpg
    145.4 KB · Views: 50
Before doing anything else, the first thing I'd be doing would be a Ze test on that supply earth.....just to be sure.
As dave said earlier, checking the bonding is very important....second thing on the list.
 

Reply to DNO UK power networks changed incoming overhead and now have PME TN-C-S but ccu connection to TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Morning guys, Just been to look at a CU change and there was a bit of an oddity with the PME connection in the old black cut out. Looking at the...
Replies
2
Views
651
Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...
Replies
3
Views
1K
I am doing a new consumer unit install on a second story ex council flat. I’ve notice the mains come in in metal conduit with no CPC. On checking...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock