- Reaction score
- 7,763
to late now the horse has bolted .We do put down for mechanical protection also along with rcd/RCBO protection. Sorry I didn't explain fully, I should of put it.
Discuss Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net
to late now the horse has bolted .We do put down for mechanical protection also along with rcd/RCBO protection. Sorry I didn't explain fully, I should of put it.
Yes and the current edition/amendment just like all the other editions/amendments, states installations constructed to earlier editions may not necessarily be unsafe.
Failure to take on board this fact, is failure to conduct the inspection in accordance with the current edition/amendment of BS7671.
We do put down for mechanical protection also along with rcd/RCBO protection. Sorry I didn't explain fully, I should of put it.
Looks like the thunder has arrived.
At least here it has.
Not very practical the inspector should be able to carry out this kind of work unsupervised or shouldn't be doing itthe Q/S should be their with the persons who is testing it .and over seeing the testing
It doesn't matter whether it excuses compliance with current Regulations.
The fact remains that the IET are never going to say that a situation which was deemed safe in previous editions is now unsafe. (The legal ramifications would be enormous.)
BS7671 requires us to make observation on non-compliances which may give rise to danger.
If the Regs. do not consider a non-compliance which complied at the time of construction to be unsafe, how can you then state the situation is potentially dangerous?
No it doesn't. That would be ridiculous. When they were installed does not materially alter their safety now.As for determining a code, that depends on when they were installed
What editions permitted bare conductors on cleats and in wooden containment? Single insulated conductors yes, but bare conductors?Bare conductors on cleats complied with a previous edition...
Bare conductors encased in a wooden moulding complied with a previous edition.
Bare conductors are allowed now, as is wooden containment.What editions permitted bare conductors on cleats and in wooden containment? Single insulated conductors yes, but bare conductors?
What editions permitted bare conductors on cleats and in wooden containment? Single insulated conductors yes, but bare conductors?
for what reasonIf an installation has been installed to a previous addition of BS7671 eg 15th/16th and still complies with that edition should not make the installation warrant a C1 (danger present .risk of injury immediate action required ) or C2 (potentially dangerous) the standard of additional safety of which electrical installations are installed to has changed/improved .Other regulations eg H & S acts may come into play and require RCD protection. I can't see what Part P has to do with a EICR however if I am correct it comes into play if certain work is undertaken when the domestic and business premises share the same meter.
Lol, you can purchase modern day wooden fronted accessories:
Classic 2 Gang 13Amp Switched Socket in Solid Oak [CXC06-2-OBK] - £15.99 - http://www.switchtowood.co.uk/shop/index.php?main_page=product_info&products_id=93&cPath=4&gclid=EAIaIQobChMI4bTFoMKV1QIVpL_tCh1mmgDJEAQYASABEgKdyfD_BwE#googlebase
Reply to Do socket outlets in a Pub need to be RCD/RCBO protected! in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.