Discuss Do split phase boards exist? in the Commercial Electrical Advice area at ElectriciansForums.net

gazj82

-
Reaction score
132
Living out in the sticks. I have come across old split phase installations a few times and done a little maintenance on them. These installations usually consist of a old 3 rewireable db with only 2 phases used.

Well for the first time I have been asked to add some circuits which requires a new board. Do split phase boards exist? Or do I follow the convention of old and just use a 3 phase board and only connect my 2 phases in the bottom of the main switch? Obviously clearly marking on the front of the board that it is not connected in the standard convention.
 
Are you sure it is true split phase and not just two from three? If so, your going to have real trouble finding LV dis boards rated above 400/415V at 460/480V
 
I've never seen a board that was manufactured as a split phase board. Specifying suitably rated components can be a a problem with the higher phase to phase voltage.

*edit* Beaten to it by Mr Skelton who obviously uses more than one finger when typing :)
 
It could well be 2 from 3, rather than split phase at 180o. Either way still need to know if using a 3 phase board is acceptable on a 2 phase system. I must admit I hadn't thought about boards not being rated for 480v.
 
It could well be 2 from 3, rather than split phase at 180o. Either way still need to know if using a 3 phase board is acceptable on a 2 phase system. I must admit I hadn't thought about boards not being rated for 480v.

If it is just two from three you can use what you like. Use a SP DB with a three pole instead of two pole isolator (providing voltage rating is appropriate) or a TP DB with two phases linked within.

If it is indeed a split phase supply which I highly doubt you may find yourself up poo creek withou a paddle when it comes to an all inclusive distribution arrangement. Keep both phases split from the head and kept as two entirely seperate phases.
 
Thanks that helps loads. If it is indeed split phase then I could install 2 single phase boards to keep my loads balanced. Just seems a little silly, especially as the future could hold an upgrade to 3 phase. If it is indeed 2 derived from 3 then I'll go with a 3 phase board from the go.

Thanks for you help :)
 
If it is indeed 2 derived from 3 then I'll go with a 3 phase board from the go.

It's your call and no one would fault your choice but you'll find that a split load single phase board and three pole isolator is a lot cheaper. Save yourself a few quid for down the pub!
 
It's your call and no one would fault your choice but you'll find that a split load single phase board and three pole isolator is a lot cheaper. Save yourself a few quid for down the pub!

I didn't get what you mean the first time round, then this post made it just click. That is an excellent idea and much better than two boards :) I had visions of double pole busbar for some reason. On a side note I have installed a merlin gerin double pole busbar board on a 110v system before many years ago when I was an apprentice. Not sure if they still exist or what there voltage rating was?
 
You can build your own 2 tier board and mark as necessary. A few manufacturers sell design and build parts for your own set-up... last one i did was a 2 tier board with on peak at top and off peak along bottom.
 
The stupid thing is that the cut out and meter ratings are only 400/415v. So why do we worry? If they give you 480v but just use there ordinary set up. I've looked but not found any special precautions or guide lines to follow.

P.s. Split is common around areas I work but some guys never see it and say "are you sure??" As if you're seeing things.
 

Reply to Do split phase boards exist? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
630
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
844
Hi Looking at a job currently adding a 3 phase solar installation but the distribution board is full obviously a new board is the best option but...
Replies
9
Views
1K
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
957
Hi guys, So, a friend of mine has a three phase 100a supply and wants to install 2 x three phase 20a fork lift chargers and a three phase car...
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock