- Reaction score
- 5,852
Add in Rolec's EVWP0020 to add a bit more confusion to the mix.
Discuss Does a three-pin socket used for Electrical Vehicle charging need a earth electrode or open PEN fault detection device? in the UK Electrical Forum area at ElectriciansForums.net
Isn't that one just a glorified socket and RCBO?Add in Rolec's EVWP0020 to add a bit more confusion to the mix.
Agreed - I seem to recall you saying you can actually see yours in genuine, which is a lovely luxury...Should be genuine TNS added to the list above.
Yes, it is but there are little buggies which charge from standard socket. Hopefully, they phase out the socket chargers and standardise the type 2. They are mainly for carrying stuff in short distances but still classed as an EV.Agreed - I seem to recall you saying you can actually see yours in genuine, which is a lovely luxury...
My conclusion for now is that as @Julie points out it's really undesirable to be regularly charging an EV with a 13A socket in the first place, so the confusion (at least on my part) on how the regs apply to the worst way to charge an EV is pretty academic.
I don't think so, they provide 230v to the car itself, so there is no guarantee that is class iiIt is slightly bizarre as the risk from a EV charger relating to use with a PEN is nothing to do with the charging, it is the big lump of metal on the CPC that someone might be washing outside. Dedicated high-rate charger or 13A plug I'm not sure there is a difference here.
But...is there? Do cars charging from a 13A/16A outlets actually use double-insulated (class II) systems so the PEN-connected-CPC is irrelevant?
Agree with Julie. Worth pointing out that i see a lot of burned out sockets as they just cant handle a prolonged load for several hoursNo, as far as the regs are concerned it's just a standard outlet (requiring rcd etc).
However I think 'granny chargers' should be prohibited as they don't properly provide the protection normally afforded by a normal charge point, and they run at 100% load permanently - not really the sort of load expected on a 13A socket outlet.
So it would be good practice to add it, but the danger is the outlet may be used for 'normal' loads which would be better on tcns
Reply to Does a three-pin socket used for Electrical Vehicle charging need a earth electrode or open PEN fault detection device? in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.