Search the forum,

Discuss Dual rcd board tt system in the UK Electrical Forum area at ElectriciansForums.net

dnjr

-
Reaction score
56
Dear all
Wonder if anyone can enlighten me
I've just changed a board to a dual rcd board. TT system with ze of 100 ohms
All circuits test ok and everything fine for 2 days . Had a call to say that while the customer was out ( so nothing in use) both rcds tripped at same time , they know this as two timer clocks ( one on each rcd side stopped at same time)
As far as I know it's only happened one , customer has asks what would cause it and I don't know so thought I would ask. I'm guessing it's something external but would appreciate anyone who can enlighten me
Cheers


Sent from my iPad using Tapatalk
 
Had a call to say that while the customer was out ( so nothing in use) both rcds tripped at same time , they know this as two timer clocks ( one on each rcd side stopped at same time)

Just because the customer was out, doesn't mean that nothing was 'in use'. At the very least there were two clocks!

Central heating (incl water heating), fridge and freezer are an obvious starting point.
 
Just because the customer was out, doesn't mean that nothing was 'in use'. At the very least there were two clocks!

Central heating (incl water heating), fridge and freezer are an obvious starting point.

tripping both rcds?

Has the OP got a earth clamp meter? Thats where I would start!
 
Just because the customer was out, doesn't mean that nothing was 'in use'. At the very least there were two clocks!

Central heating (incl water heating), fridge and freezer are an obvious starting point.

Hi handy sparks. Thanks for the reply
Boiler switches off at 9 and rcds tripped at 10.30 so can't be that, fridge and freezer are on same circuit so only one rcd would trip. Just very strange they both went at same time
There is a time clock on each circuit but them both to fault at same time would be amazing . More chance of England winning euros I would think


Sent from my iPad using Tapatalk
 
tripping both rcds?

Has the OP got a earth clamp meter? Thats where I would start!

Hi Murdoch. Yep have a clamp meter / tong type , not been asked to go back as yet as its only tripped once. They asked me why it would happen , I'm not too sure so thought I would ask those more learned than myself.


Sent from my iPad using Tapatalk
 
Hi murdoch. Have already asked them to keep a log. Man of the house is onto it, said he had a notebook that would be just the job. No thunder or lightning or local road works etc.. Thanks for replies watch this space..


Sent from my iPad using Tapatalk
 
could be due to these:

gremlins.jpg
 
Standard dual 30mA rcd board with 100A main switch. Not much experience of TT systems. Wrong ?


Sent from my iPad using Tapatalk

Not wrong, I haven't done an AMD3 CU TT change since the metal boards came about so I was just wondering whether you had fitted the RCD in place of the isolator.

This isn't a trick question or point BTW

I've got a TT CU change to do soon so just wondering what other people do!

I fit RCBO boards normally so I will need to change the 100A isolator for a RCD to achieve DP isolation
 
Last edited by a moderator:
Would only need up front s type, if the installation has a distribution circuit, simple tails and and bespoke gland would suffice, I believe. As regards fault youve had, read here loads of different possibilities. Might be some paths for you to follow, if you search below.
 
Not wrong, I haven't done an AMD3 CU TT change since the metal boards came about so I was just wondering whether you had fitted the RCD in place of the isolator.

This isn't a trick question or point BTW

I've got a TT CU change to do soon so just wondering what other people do!

I fit RCBO boards normally so I will need to change the 100A isolator for a RCD to achieve DP isolation

Just out of curiousity will you be using RCBO's on that board change? If Single Pole Solid Neutral ones, an N-E fault would take out the time delay RCD
 
Dear all
Wonder if anyone can enlighten me
I've just changed a board to a dual rcd board. TT system with ze of 100 ohms
All circuits test ok and everything fine for 2 days . Had a call to say that while the customer was out ( so nothing in use) both rcds tripped at same time , they know this as two timer clocks ( one on each rcd side stopped at same time)
As far as I know it's only happened one , customer has asks what would cause it and I don't know so thought I would ask. I'm guessing it's something external but would appreciate anyone who can enlighten me
Cheers


Sent from my iPad using Tapatalk
Dear all
Just thought I would update this one
Surprise suprise. Owner had done sone diy after I left and borrowed a neutral for his garage lighting so when turned on a light inside it tripped both rcds. Gota love em. Cheers for replies
 
Hi lee. I though s type were not intended for Personal shock protection as they are slower to react and could allow current to flow for an unacceptable period of time. Is this not the case ?
 
Ideally there should be an up front 100mA S type RCD to provide fault protection for the links between the main switch and RCD's.
Would only need up front s type, if the installation has a distribution circuit, simple tails and and bespoke gland would suffice, I believe.

Lee's correct again, when using A3 Dual RCD CU on TT :(. Apart from I thought the page number was 32-35 yellow OSG ;) (haven't got a yellow one yet myself), which advices using s type as main switch.
 

Reply to Dual rcd board tt system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
406
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
3K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
588
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top