thunder

i had a utitlity engineer checking my appliances, during the visit he did an earth loop test (tester) using the sockets, he advised me that the rea ding was too high should be 1ohms, but mine was much higher and advised me to check itout with an electrician and to hava RCD install for the r circuits i need to know the following

what should the earth loop reading be on a domestic uk household

if higher than 1 ohms what is the cause of the problem

can this be dangerous

i have earth coming oit om c unut and all pie works etc are earth bonded

many thaks
 
i had a utitlity engineer checking my appliances, during the visit he did an earth loop test (tester) using the sockets, he advised me that the rea ding was too high should be 1ohms, but mine was much higher and advised me to check itout with an electrician and to hava RCD install for the r circuits i need to know the following

what should the earth loop reading be on a domestic uk household

if higher than 1 ohms what is the cause of the problem

can this be dangerous

i have earth coming oit om c unut and all pie works etc are earth bonded

many thaks

What is your earthing system ?
What was the reading result he took?

Do you have a earth rod outside if so you are on a TT system which would explain the high efli.
If you are on a TT system he's right you need a 30mA rcd for the socket circuits & 100mA td (s type) rcd for all other circuits (this can be as the main switch or upstream of the consumer unit on the tails)

Max efli allowed will differ depending on the type on overcurrent protective device in use, for an mcb its 1.2 (corrected).

You are best to get a sparks in because without the test equipment theres sod all you'll be able to do.
 
Re: earth loop

thanks for the reply and your input

i do not think i have a earth rod

all earth links coming via consumer unit,

i may be incorrect, how can i tell

earth reading 105.4 ohms
 
Re: earth loop

thanks for the reply and your input

i do not think i have a earth rod

all earth links coming via consumer unit,

i may be incorrect, how can i tell

earth reading 105.4 ohms

From the consumer unit does the main earth cable go outside to a rod thats buried (TT system)
or down to where the electricity suppliers fuse is (TNC-s system)
or all the way down to the lead sheath of the incomming electricity supply cables (TNS system).

With a loop reading of 105.4ohms it's looking like you have a TT earthing system.

Best advice would be to get a sparks in to take a look or undertake a periodic inspection (normaly start at £150).
 
Re: earth loop

i dont think it is a TT earthing system , as i dont have an outside rod, maybe it is a tnc system, as cables are running from norwebs fuse - by having a higher ohms reading

is it dangerous, what are the consequenses, i have live in this property for nearly 10 years and had no problem as yet, as i have advised only found this out during a routine check


many many thanks, your advise is greatly valued.

thank you
 
Re: earth loop

problem sloved, called out a spark, happened to know him, the problem was the earth connection from the suppliers fuse unit to the earth supply going into cons unit, rewired the earth connection - tested reading on diff circuits - now showing 0.46 ohms
 

Reply to earh loop in the Electrical Forum Canada area at ElectriciansForums.net

Similar Threads

Good morning all, We need a little bit of advice; we are looking to buy a property, and during one of the visits, the owner told us that he...
Replies
21
Views
4K
Hi I don’t know how resolve this so any helpful advice would be greatly appreciated. I have no electrical knowledge. I will try to be as clear...
Replies
57
Views
11K
I was asked to install a small consumer unit at the end of step down transformer. The consumer unit is fed from a panel board put in place for a...
Replies
16
Views
3K
NICEIC Certification Scheme NICEIC approved contractor first visit
Info for anyone currently looking to join, Whilst I was very nervous the night before, there is no need to be, as long as you know how to test...
Replies
18
Views
10K
I have been trying to replace a CU on a domestic property. During my initial checks, there was no isolator and the earth was only 6mm on a...
Replies
29
Views
4K
YoungScud
Y

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock